I'm trying to make sense of the PID2 instruction block, and associated code for a number of extruder heat control zones (some heat only; others are heat and cool - all are time-proportioned). This control system was built
to spec almost a year ago, but operators tell me control has always been a bit odd, and today I started to delve into it ... and have gathered a
bagful of questions.
Two things that I suspect are causing problems happen because the PID2 block is enabled all the time (even when the MCR relay is opened, and when
the "Auto Control On/Off" bit from the HMI is switched to off (which opens the circuit to the output relay within the program). I'd have to think this would allow the integrating term to wind up to the endstop, and indeed one of the reported symptoms is overshoot upon startup.
However, one of the other symptoms is that the die zones are slow to heat up, and I confirmed this (at least, to the HMI level) ... for a setpoint of 410F and measured value of 150F the displayed percent output was 75%. The PID values are brought out to the HMI, and changing the proportional term to any value within the acceptable range of 5 to 500% had no effect ... I
still need to open up the HMI software, and confirm that the values on the HMI screen are pointing to the correct registers.
Another observed symptom is that control is acting almost in limit fashion for the heat/cool zones. When slightly above setpoint cooling turns on to 100%, and slightly below setpoint heat turns on 100%. I can play with the PID values 'till cows show up in the driveway without changing the displayed % output one whit. Yet another symptom is that (when everything
settles down) the measured value can be quite far away from setpoint (on the order of 10 to 20 degrees), and doesn't prompt any correction.
I found another problem (in HMI coordination) because the upper allowed setpoint values for I and D are limited to 9999 (but values of 10000 or
above turn off these terms, per chapter 21.2 in 840 USE 101 00 documentation), so I couldn't troubleshoot using proportioning only. I've done PID using A-B processors (usually SLCs), but not on the Quantum 424 this machine is using, so maybe I'm just "not getting it", but the time
proportioner coded in this program doesn't look like it could ever have worked very well (I'm still digging into it ... don't want to cast
aspersions towards the original programmer given my inexperience).
I'm hoping that someone else has written a time proportioning heat controller built around the PID2 that they'd be will to place into PDF
format, and submit to the PLC archive. The Modicon tech I was talking to earlier today is supposed to be e-mailing me a sample as well, but I'd just as well have several different approaches to look over and learn from.
One of the things neither I nor the tech could find was how the high and low integral windup parameters (4x9 and 4x10, respectively) are operated on within the PID block (they aren't shown in the block diagram on page 403 of
manual 840 USE 101 00). The explanation on page 407 is rather terse, but (in the case of the barrel zone I was concentrating on) these values are 4000 and 200, and, if I'm reading this correctly, setting the lower anti-windup to 200 effectively kills integration when the output is less than 200/4095 (4.9%). This doesn't look too kosher to me ...
When I tried to edit the programming (to disable the PID block when appropriate to do so) ProWorx NxT returned a message 389 "Command Not Valid
Unless Logged In." The on-line help was of no help, and I didn't see any menu options related to logging in. I'm guessing the processor thinks it's networked, and someone else is programming on it. Anybody know what's up with this?
This processor has three DB-9 comm ports. COM1 is used to communicate to the HMI, and COM2 and COM3 are open. COM3 is Modbus+, and COM1 and COM2 are
Modbus.
When I connect up to COM2 it appears to see the processor, but returns a "Timeout During Receive" error (#364) if I attempt to go online. If I use
COM1 I can go online (but, of course, the HMI is now unplugged). The front panel RTU/ASCII switch is set for RTU. The documentation in 840 USE 100 00 doesn't go into detailing differences between COM1 and COM2 ports. Can anybody suggest why the above occurs, and point me to a reference source that speaks on this issue?
BTW - temperature feedback comes from ATI 030 00 thermocouple modules.
Thanks in advance,
Bob
to spec almost a year ago, but operators tell me control has always been a bit odd, and today I started to delve into it ... and have gathered a
bagful of questions.
Two things that I suspect are causing problems happen because the PID2 block is enabled all the time (even when the MCR relay is opened, and when
the "Auto Control On/Off" bit from the HMI is switched to off (which opens the circuit to the output relay within the program). I'd have to think this would allow the integrating term to wind up to the endstop, and indeed one of the reported symptoms is overshoot upon startup.
However, one of the other symptoms is that the die zones are slow to heat up, and I confirmed this (at least, to the HMI level) ... for a setpoint of 410F and measured value of 150F the displayed percent output was 75%. The PID values are brought out to the HMI, and changing the proportional term to any value within the acceptable range of 5 to 500% had no effect ... I
still need to open up the HMI software, and confirm that the values on the HMI screen are pointing to the correct registers.
Another observed symptom is that control is acting almost in limit fashion for the heat/cool zones. When slightly above setpoint cooling turns on to 100%, and slightly below setpoint heat turns on 100%. I can play with the PID values 'till cows show up in the driveway without changing the displayed % output one whit. Yet another symptom is that (when everything
settles down) the measured value can be quite far away from setpoint (on the order of 10 to 20 degrees), and doesn't prompt any correction.
I found another problem (in HMI coordination) because the upper allowed setpoint values for I and D are limited to 9999 (but values of 10000 or
above turn off these terms, per chapter 21.2 in 840 USE 101 00 documentation), so I couldn't troubleshoot using proportioning only. I've done PID using A-B processors (usually SLCs), but not on the Quantum 424 this machine is using, so maybe I'm just "not getting it", but the time
proportioner coded in this program doesn't look like it could ever have worked very well (I'm still digging into it ... don't want to cast
aspersions towards the original programmer given my inexperience).
I'm hoping that someone else has written a time proportioning heat controller built around the PID2 that they'd be will to place into PDF
format, and submit to the PLC archive. The Modicon tech I was talking to earlier today is supposed to be e-mailing me a sample as well, but I'd just as well have several different approaches to look over and learn from.
One of the things neither I nor the tech could find was how the high and low integral windup parameters (4x9 and 4x10, respectively) are operated on within the PID block (they aren't shown in the block diagram on page 403 of
manual 840 USE 101 00). The explanation on page 407 is rather terse, but (in the case of the barrel zone I was concentrating on) these values are 4000 and 200, and, if I'm reading this correctly, setting the lower anti-windup to 200 effectively kills integration when the output is less than 200/4095 (4.9%). This doesn't look too kosher to me ...
When I tried to edit the programming (to disable the PID block when appropriate to do so) ProWorx NxT returned a message 389 "Command Not Valid
Unless Logged In." The on-line help was of no help, and I didn't see any menu options related to logging in. I'm guessing the processor thinks it's networked, and someone else is programming on it. Anybody know what's up with this?
This processor has three DB-9 comm ports. COM1 is used to communicate to the HMI, and COM2 and COM3 are open. COM3 is Modbus+, and COM1 and COM2 are
Modbus.
When I connect up to COM2 it appears to see the processor, but returns a "Timeout During Receive" error (#364) if I attempt to go online. If I use
COM1 I can go online (but, of course, the HMI is now unplugged). The front panel RTU/ASCII switch is set for RTU. The documentation in 840 USE 100 00 doesn't go into detailing differences between COM1 and COM2 ports. Can anybody suggest why the above occurs, and point me to a reference source that speaks on this issue?
BTW - temperature feedback comes from ATI 030 00 thermocouple modules.
Thanks in advance,
Bob