Need to know of any transmitters out there that can take a 0volt to 8volt non-linear signal and convert it to a linear 4ma to 20ma signal or 0volt to 10volt linear signal.
By Karppi, Dan \(SudburySmelter\) on 5 October, 2003 - 5:27 pm
AJ,
Have a look at this instrument. It might be what you need.
http://www.alphacontrols.com/Inor/86DIQ00022.pdf
Dan
Dan Karppi CCST III
Falconbridge Limited
Falconbridge, Ontario
Canada
P0M 1S0
By Curt Wuollet on 5 October, 2003 - 6:21 pm
That would be a most interesting device for
an arbitrary non-linear signal. A PIC or
similar with an ADC a lookup table and a DAC
would probably be the closest practical thing.
cww
This is exactly what a thermocouple transmitter does. If you have a plot, a transmitter company should be able to make one for you.
By Thomas Hergenhahn on 5 October, 2003 - 7:02 pm
This cannot be answer without knowing what kind of non-linear signal you have. There are, for example, converters for the squareroot function, which occurs e.g. in flow measurement.
There are converters for the non-linear signals of every kind of thermocouples.