DCS system
Anonymous
What is the best dcs solution for a petrochemical plant utility? Utilities like water supply, water treatment, N2, F&G, power substation, etc.
We have used both Delta V and Matrix Total Control at our Plant. Both are very similar and easy to work with.
ControlNovice
If the facility has an existing DCS system for the Process side, you may want to tie into it. If so, it may be best to keep the same style DCS.
If you really don't need to tie into an existing system, then for Utilities, you really only need a PLC and HMI's. The expense of a DCS is overkill (in general) for these types of services. Also, the utilities you mentioned are rarely in the same area of the plant, so individual PLCs may work better, each located in the section you are monitoring/controlling.
Yokogawa's CS3000 DCS system is probably the best solution. Newly released controller (FFCS) is both powerful and cost effective, and can communicate to most devices. (Fieldbus, Profibus, Modbus, OPC, etc.)
What DCS is installed as main control?
ABB System 800XA; Fully open; complies with IEC-1131 and communicates Profibus, FF HSE, HART, etc....
ABB Freelance AC800F is the best solution which provide easy Engineering & Configuration on one window with easy Control Builder F.