Modbus Error Code

M

Thread Starter

Mike_t_m

I would have a list of Modbus Error Code and of course, measure note for the codes, please.
 
HEX Error Code for Modbus Plus and SY/MAX Ethernet:
Hex Error Code Meaning
1001 User has aborted the MSTR element
2001 An unsupported operation type has been specified in the control block
2002 One or more control block parameter has been changed while the MSTR element is active (applies only to operations that take multiple scans to complete). Control block parameters may be changed only when the MSTR element is not active.
2003 Invalid value in the length field of the control block
2004 Invalid value in the offset field of the control block
2005 Invalid values in the length and offset fields of the control block
2006 Invalid slave device data area
2007 Invalid slave device network area
2008 Invalid slave device network routing
2009 Route equal to your own address
200A Attempting to obtain more global data words than available
30ss Modbus slave exception response
4001 Inconsistent Modbus slave response
5001 Inconsistent network response
6mss) Routing failure


ss HEX Value in Error Code 30ss
The ss subfield in error code 30ss is:
ss Hex Value Meaning
01 Slave device does not support the requested operation
02 Nonexistent slave device registers requested
03 Invalid data value requested
04 Reserved
05 Slave has accepted long-duration program command
06 Function can’t be performed now: a long-duration command in effect
07 Slave rejected long-duration program command
08 ... 255 Reserved


--------------------------------------------------------------------------------

ss Hex Value in Error Code 6mss
The m subfield in error code 6mss is an index into the routing information indicating where an error has been detected (a value of 0 indicates the local node, a 2 the second device on the route, etc.).
The ss subfield in error code 6mss is:
ss Hex Value Meaning
01 No response received
02 Program access denied
03 Node off-line and unable to communicate
04 Exception response received
05 Router node data paths busy
06 Slave device down
07 Bad destination address
08 Invalid node type in routing path
10 Slave has rejected the command
20 Initiated transaction forgotten by slave device
40 Unexpected master output path received
80 Unexpected response received
F001 Wrong destination node specified for the MSTR operation
 