Why is current transformer secondary short circuited during the operation?
By Anonymous on 6 June, 2007 - 11:47 pm
The current transformer secondary is short circuited during the operation. What is the reason, and explain with details.
By Mike Foster on 9 June, 2007 - 12:55 am
Unless a burden (i.e. meters, relays, etc.) is connected to the CT, current transformers should always be shorted across the secondary terminals. The reason is very high voltages will be induced at the terminals. Think of the CT as a transformer, with a 1 turn primary and many turns on the secondary. When current is flowing through the primary, the resulting voltage induced in the secondary can be quite high, on the order of kilovolts. When a CT fails under open circuit conditions, the cause of failure is insulation breakdown, either at the shorting terminal strip, or at the feedthrough (in the case of oil filled apparatus), because the distances between terminals are not sufficient for the voltages present.
By Anonymous on 19 July, 2007 - 5:32 pm
The next question is how does it work so by shorting the secondary terminal of CT, there's no over-voltage happen?
By Curt Wuollet on 21 July, 2007 - 12:17 pm
Because you typically develop little voltage across a short or the reflected impedance of a short.
cww
CT is connect in series with the load, when CT is shorted or connected to certain load, the impedance become negligible compared to circuit its connected, so voltage drop across CT will be negligible.
When CT gets open circuited, the impedance of CT become infinity, hence the voltage drop across CT primary will try to rise up to to the rated supply voltage, but in this process insulation fails.
CT secondary will develop a very high voltage when secondary is open circuited with the primary energised. But if the CT secondary is kept open initially and the primary is energised, will the CT get damaged?
It is all flux theory of transformer taught us in school, i.e. if open secondary, no opposition to primary flux and increases tremendously.
By vijayamurugan on 20 October, 2011 - 8:21 am
of course, definitely the coils of CT will get damaged.
CT primary energised also secondary energised, but open circuited what will happen. it will burn.
By Patric Bernard on 28 November, 2012 - 3:42 pm
Depending on how long the secondary is kept open, not necessarily. This is exactly how Spark Plugs work in a car, and have worked for... well almost forever. The Secondary coil of the ignition coil, or the distributor, opens, causing a high voltage build up in the Primary, When the Secondary closes again,the extremely high voltage transfers to the secondary, and finally across the spark plug gap to ground, causing the spark in the spark plug, and that happens to the spark plugs/coil thousands of times a minute in some cases.
By A NAranjo on 13 July, 2017 - 11:08 am
You are missing a very important fact. In ignition coil the voltage raises tremendously additionally because the speed of contracting magnetic field due the presence of condenser connected in parallel to the contacts (old systems) or solid state switches (modern system) when they open.
why voltage not high when we short the C.T secondary side?
Pls explain with principle.
Basic formula, V=IR.
Voltage is directly proportional to resistance with constant I. Remember that voltage also known as potential energy (voltage drop only happen when there is difference in voltage between two point!). So when we short the wires, there is no resistance exist (or negligible value resistance of wire). Meaning no voltage occur between the joined wire.
By KTS.MURTHY on 4 October, 2007 - 9:39 pm
CT secondary current is based on primary current (based on load). As per CT design, when CT shorted condition voltage is limited, if CT is open current is zero, voltage will be very high, during this time CT will burnt.
Basically a ct is a step up transformer, normally in the primary of a ct high currents are flowing. If the secondary is opened then as it's a step up transformer.
A high voltage is induced in the secondary, the induced secondary voltage is very high, it may damage the instrument itself or it may damage the observer or the insulation may break down so it must be shorted with an ammeter of suitable range or must be shorted.
As we know that, CT works as step up transformer because the voltage induced across the secondary terminal is so high in terms of Mv. So if the secondary will open, its insulation can not bear the pressure of voltage it will fail, due to that fire will occurs. So during the installation time, secondary of CTis short circuited. Due to short circuit the voltage across the secondary will become zero and current become maximum, and we know that the current is very low in this case.
actually the voltage ratio is just opposite to the current ratio means: if there is 1000 amp in the primary side then it would be 1000 on the secondary also 1000/1,rather being n a step down. X-mer so the ends are short circuited !!!
(CT) is a type of instrument transformer specially designed for protection and measuring purpose, it will operate by the current whenever it exceeds the set value. The C.T converts the 1000A/5A. In the secondary more tappings we will take depend upon the measurement. then Electrons will flow in the closed path only. So the secondary will short circuited.
By Colin Dedman on 20 October, 2011 - 11:53 pm
Most replies answered by pointing out that destructive voltages will be generated if the secondary is open-circuited. While this is true, it does not exactly answer the question.
A current xformer will still operate safely over a wide range of secondary load resistances, so why is a very low secondary load resistance (= approximately a short circuit) the best choice?
The reason is that the fidelity of the current transformer is highest when the secondary is short circuited.
The purpose of a current xformer is to provide a scaled-down version of the primary current with the highest possible fidelity, that is, the secondary current should be a faithful replica of the primary current. In many applications it is not just the magnitude of the measured current that is important, but also faithful reproduction of the phase and high-order harmonics.
Thus, the question becomes, why is the fidelity highest when the secondary is shorted? At first this seems counter-intuitive, for the fidelity of the more familiar voltage transformer is most definitely NOT optimised by shorting the secondary! Indeed, as a voltage transformer is loaded more heavily by reducing the secondary load resistance, the secondary voltage 'sags', phase error is increased, and frequency response decreased, all leading to a loss of fidelity of the secondary voltage waveform. This occurs mainly due to winding resistance and leakage inductance, which would both be zero in an 'ideal' xformer. For a voltage transformer, the fidelity of the secondary voltage is highest with a high secondary load resistance, which draws very little current.
However, with current xformers, just about everything turns out to be reversed compared to voltage xformers, which can be confusing. As with all xformers, the secondary load resistance is reflected back to the primary side, scaled by the square of the turns ratio. Therefore, if we short the secondary, then we also short the primary. Note that the primary current is fixed and constant, being set by the external circuit. Therefore, from V=IR, the voltage developed across the primary winding is approximately zero when the secondary is shorted. Of course, the secondary voltage is also zero when shorted. But why does this improve the current fidelity? Without going into too much detail, the 'magnetising current' of an xformer depends on the winding inductance and the winding voltage. The inductance is set by the number of turns and the core material and geometry, which are fixed for any given current xformer. However, by reducing the winding voltages, by shorting the secondary, the magnetising current is also reduced to near zero. That is a GOOD THING, because the magnetising current is an error, representing a proportion of the primary current that DOES NOT end up being reflected in the secondary current. The magnetising current results in an error in both the magnitude and phase of the secondary current, definitely not a good thing where high fidelity is required. To say the same thing in a different way, shorting the secondary permits larger currents to be measured with acceptable fidelity, and without core saturation.
The conclusion is a beautiful inverse of the situation for a voltage transformer. In summary:
For a voltage xformer, the primary voltage is fixed, and the current is set by secondary load resistance. Reducing the secondary load resistance increases the current, increases the 'loading', increases the power delivered to the load, and lowers the secondary voltage fidelity. A high value of secondary load resistance is desirable for best voltage fidelity. Shorting the secondary will generate dangerous currents.
For a current xformer, the primary CURRENT is fixed, and the VOLTAGE is set by the secondary load resistance. INCREASING the secondary load resistance increases the VOLTAGE, increases the loading, increases the power delivered to the load, and lowers the secondary CURRENT fidelity. A LOW value of secondary load resistance is desirable for best fidelity. OPEN-CIRCUITING the secondary will generate dangerous VOLTAGES.
Electrical engineering ... truly beautiful.
Colin
I have a question regarding CT with tap on the secondary.
Lets assume there are 3 terminals on the secondary S1, S2 and S3. Lets also assume that between S1 ans S2 there is a nominal small load (of the protection device, S2 is connected to earth).
What about the windings between S2 and S3?
Should they be shorted in order to prevent dangerous voltage??
I do know that when there is no load on S1-S2, we have to put a short between them. So why S2-S3 shouldn't (since it has no load)!
Thanks,
Shai Halperin
Shai... in answer to your two questions about Multi-Ratio (not Multi-Winding) CTs:
1) Only one tap should be used.
2) Do not short the other.
Regards, Phil Corso
We should connect any one winding to the load or short circuit any one secondary winding, other can be kept open. There will not be any high voltage in the second winding.
Since CT is connected in series with the circuit, we have to make sure that CT secondary circuit is closed through any path and total impedance appearing across CT primary circuit is kept low.
It is just like small resistor (ct)with different tappings connected in series with heavy (load) resister in a circuit, we can use any tap to complete the circuit. if we open entire voltage will appear across the (ct)small resistor.
Sunil Kumar (Mangalore, India)
If it is multi winding (core) then unused winding should be kept shorted because its just like impedance connected in series, if any one secondary winding opens, it became open circuit and cause damage.
By sunil kumar on 3 October, 2012 - 12:38 pm
Why is not short circuit for ammeter connect secondary of current tranaformer
Thank you for the explanation.
>>Colin et al,
I have a similar question but with a little twist...
What happens to the inductance on the primary side when one of the turns is shorted on the secondary side...ie lets say you have 10 turns on primary and 100 turns on secondary and you solder turn 50 and 51 together (not to ground or anything else just each other). What happens?
Ali Ali... very good question. Essentially there are two 'negative' results for the example you cited:
1) The turns-ratio Nsec/Npri will be reduced by one turn, that is, from the normal 10:1 to 9:1. This of course will affect measurement accuracy!
2) More importantly, transformer-action will magnetically couple the 'shorted-turn' to the other 99 turns having and effective turns-ratio of 99:1. The resultant induced current in the single loop will produce localized heating that will cause additional damage to insulation, winding, dand core!
The above discussion ignores other exacerbating factors such as frequency, current wave-shape (if not sinusoidal) and capacitance, if present.
Regards, Phil Corso
Ali Ali... correction to my earlier comment:
1) Nsec/Npri ratio for shorted turn-to-turn condition should be 9.9:1!
Phil
How about the case, if CT has a test conductor (current injection through CT window) and shorted on terminals, turn ratio and accuracy will change on the secondary? and is that also necessary to short the terminals of such test conductor or leave open?
Great answer colin.
was searching something sensible for a long time..
All comments where very helpful. In addition, i think one can also use the transformation formula V1/V2=I2/I1 to quickly asses the secondary voltage V2 which is equal to V1xI1/I2. The answer is very obvious: if I2 is zero, the result is infinity. thank you.
With this, how do you explain the fact that the secondary of a PT should always be kept open? :)
Though the secondary voltage is very very high, it is not infinity and there is a correct way to calculate it. Thanks.
Well said Colin!
I must make one correction though, you stated "Therefore, from V=IR, the voltage developed across the primary winding is approximately zero when the secondary is shorted." which is a bit off. There will be no voltage developed "across" the primary winding of the CT whether the secondary is shorted or not. There will be voltage measured to ground of course, but since the primary "winding" of a CT is simply the current carrying conductor that passes ONCE through the window of a CT you will measure ZERO voltage from any place on this conductor to another on the same conductor, energized or not. I dislike the term "winding" for the primary of a CT because it is not wound at all, (unlike power transformers) and is therefore confusing, I prefer primary current to be measured and secondary winding.
Other than that small detail, nice work!
By M.jagan kumar on 24 August, 2013 - 10:15 pm
ANS:. If the transformer secondary is not short circuited, during the operation - it will opened means, it damage the coil and burnt out. It will affect the surrounding peoples also. It is very dangerous.
By JEFF JONES on 6 July, 2016 - 9:01 am
look at it like this:
a VT is a constant voltage source
open circuit- normal voltage (voltage across terminals) normal current when load applied
Short circuit - unsafe "huge currents across short"
loads must be connected in parallel not series
A CT is a constant current source
Open circuit - unsafe - huge voltages
Short circuit - safe (small volts constant current
Loads must be connected in series
I was once given the task of testing some new MCC feed breakers, the owner wanted to see them trip by injecting a high current directly across the busbars, this we did using a Variac and a 1KVA transformer rewound with just one turn on the secondary.
It all went very well until we came to one breaker where we couldn't get enough current through the busbars to exceed the breaker rating. It turned out one of the metering CTs was wired wrong and the secondary was open. There was enough impedance in the busbar primary of the CT that we couldn't get enough current through it.
If you think about the CT ratio e.g. 500:5, if you put 100 Volts across the primary you should be able to get 10,000 Volts on the secondary. I know that's pretty simplistic and completely disregarding losses but you get the idea.