Control Logix
PLCs and related questions. topic
Posted by Shehper on 8 June, 2008 - 8:49 pm
Following are my queries regarding a Control Logix SIL 2 System and panel Computers:

1. We are designing a redundant Control Logix system with redundant IOs which will be SIL 2 certified. Now we require 2 digital input modules (1756-IB16D) for our inputs. The inputs need to be time stamped so we are using 2 additional SOE modules (1756-IB16ISOE) for achieving this.

These SOE modules are in addition to the already present diagnostic digital input modules. This satisfies the SIL 2 requirement of wiring one sensor to two different inputs as stated in ‘1756-rm001_-en-p Using ControlLogix in SIL2 Applications Manual’.

We also need to provide redundancy to these IO modules. For that we have added two additional 1756-IB16D to serve the purpose.

Please suggest that keeping in view the SIL2 and IO redundancy requirements, do we need to add two additional SOE modules in addition to the first set of SOE modules as well or the two 1756-IB16D modules (making the first pair of 1756-IB16D redundant) will serve the purpose of IO redundancy and SIL 2 requirements. Please not that in the later case the SOE modules will be used for time stamping of both the sets of 1756-IB16D modules.

2. Similarly for analog inputs we are using one 1756-IF6I. Now we are adding one additional 1756-IF6I module to make system SIL2 and then another one is added for redundancy. Do we require this third module or the IF6I added for SIL 2 will be sufficient for redundancy as well keeping the SIL 2 requirements in mind.

3.Are the L6 series CLX processors SIL 2 Certified now. Similarly is Version 16 of RSLogix 5000 SIL2 certified?

4.Can we use Prosoft MV156-MCM module in IO chasis of a SIL2 system?

5.Can the ControlNet 1784-PCIC communication interface card be used in AB Panel Computers providing half length PCI slot or do we need any other module to communicate with panel computers with half length PCI slot over Control Net?

Any help in this regard will be appreciated. I can be contacted at safroze@iaef.ae


Posted by former SIL2 Sales on 12 June, 2008 - 11:02 pm
I am very interested to know the reply by RA on question 2. As for Prosoft, if you refer to
http://www.tuv-fs.com/CLX_SIL2_Revision_List_P4.pdf
there's no listing of this module so what does it mean ? SIL2 or not SIL2? Maybe you should think of using ControlNet as the LAN.
One question for RA, is it true that the GuardPLC SIL3 is OEM from Hima ?

SIL2 Safety PLC nowadays is getting more potential - you have RA with ControlLogix, Modicon - Quantum, MTL-SafetyNet,Detronics - ELS


Posted by Nick Mellor on 3 July, 2008 - 11:03 pm
Hi,

Please bear in mind that achieving SIL 2 certification will require much more than a SIL2 or 3 certified PES. SIL verification is required for SIFs which have been identified, and that includes your sensors and final elements.


Posted by SIL2 on 6 July, 2008 - 3:46 pm
Hi,
You are right. SIL should be certified for the whole loop (sensors/instruments -> PES). Recently I come across surge protection device that was SIL 'suitable'. I think from MTL.

Thanks

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!