Mark V persistent diagnostic alarms
Applications topic
advertisement
Posted by AZIR on 3 July, 2008 - 1:25 am

In our GE Gas Turbine Mark V TMR system, the following Diagnostic Alarms are persisting. Could anyone please guide me to locate where is the problem? I understand these alarms are from P-Core <Y> for S-Core controller.


C 2355 Voter Mismatch (S) L28FDD
C 2362 Voter Mismatch (S) L52B_SEL
C 3799 Voter Mismatch (S) SFL1
C 2352 Voter Mismatch (S) L28FDA
C 2354 Voter Mismatch (S) L28FDC
C 2353 Voter Mismatch (S) L28FDB
C 2377 Voter Mismatch (S) L4PTR2_FB
C 3795 Voter Mismatch (S) TNH_OS
R 1697 TCE1 TMR check trouble, ETR2
R 1696 TCE1 TMR check trouble, ETR1
C 2375 Voter Mismatch (S) L4ETR2
C 2374 Voter Mismatch (S) L4ETR1
T 1697 TCE1 TMR check trouble, ETR2
T 1696 TCE1 TMR check trouble, ETR1
C 3798 Voter Mismatch (S) SFDIFF1
C 3797 Voter Mismatch (S) SSDIFF1
C 2370 Voter Mismatch (S) L30AS3
C 2369 Voter Mismatch (S) L30AS2
C 2368 Voter Mismatch (S) L30AS1
C 2366 Voter Mismatch (S) L14L_ZE
C 2364 Voter Mismatch (S) L12L_P
C 2363 Voter Mismatch (S) L12H_P
C 2361 Voter Mismatch (S) L4_FB
C 2360 Voter Mismatch (S) L5E_TCEA

Posted by CSA on 3 July, 2008 - 10:47 pm
What have you done to try to troubleshoot the problem?

Have you looked at any of the signals in the Prevote Data Display?

When do these alarms occur? During starting? If so, when? At breaker closure? When the unit is on line? Is the unit a generator drive or a mechanical drive? What kind of turbine is it?

Posted by azir on 5 July, 2008 - 11:45 am
Still, I am yet to change any modules etc. The Prevote display shows that different S core than that of R and T core. i.e., if R and T are 1 then S is zero.

These alarms appear when the conditions occur. for example, the L28FDs appears when flame conditions are satisfied and resets on unit shutdown.

And few alarms are persisting always.
It is a GE Frame 7EA machine.

Regards

Posted by CSA on 5 July, 2008 - 3:04 pm
Which values in <S> are different from <R> and <T>? Of course, if <S> thinks the unit should be tripped and <R> and <T> don't then it will have different values that <R> and <T>, which is kind of what these alarms are telling you. Some input to <S> is causing <S> to believe that the unit should be tripped. If <S> thinks the unit should be tripped and it sees flame, that's also a problem. Without good data, there's not much we can do to help you.

If you want real help with these alarms via this forum, you are going to have to provide more details. Which alarms are persistent? What are the data values when the alarms are annunciated?

I'm not really clear what you mean by alarms appear when conditions occur and the L28FDs appear when flame conditions are satisfied. Are you trying to say that the L28FD voting mismatches occur when flame is established during starting and then when the unit is shutdown the alarms clear? If so, this is a pretty big clue to the problem! Loss of flame indication to any processor is a pretty big problem.

Have you looked at the cables in the <P> core--the ones that connect the PTBA terminal board to the TCEB and the TCEAs? Are they all inserted correctly? Are the LEDs on the TCEA cards in the <P> core all flashing the same sequences, or does <Y> flash a different sequence than <X> and <Z>? You can see how the cables interconnect the components by looking at the Signal Flow Diagrams in Appendix D of the Mark V Application Manual, GEH-6195.

These types of problems can sometimes be caused by problems with the ribbon cable connectors/pins becoming "corroded" and can be corrected by the application of some conductive grease on the connectors. There are usually tubes of conductive grease provided in the boxes with spare Mark V cards.

I really think you need to have someone knowledgeable in Mark V troubleshooting visit the site and help analyze and resolve the situation. Many times, there's no need to replace components (actaully, there's an awful lot of unnecessary card-swapping and servo replacement going on all the time around the world!).

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!