reasons for flashover
Motion control, servos, steppers, etc. topic
Posted by paru on 27 July, 2008 - 11:56 am
Few months back we had a flash over on the surge arrestor on primary side of power transformer. There is a network of surge arrestor connected in delta for phase to phase and in star for phase to line.
can overvoltage create this problem? or there are some other reasons?
Posted by Otpidus on 29 July, 2008 - 12:43 am
Power transformers normally experience huge surges during switching on. You have not mentioned trafo ratings and voltage levels, but I would suggest to check the switching breaker especially the bounces during closing. A particular phase with high bounce will induce surges in other two phases and can damage the surge arrestors.
Posted by pk on 30 July, 2008 - 11:06 pm
It is 125MVA trafo with 33kv on its primary side where the surge arrestor are connected. Same time when the flashover occurred there was some flash over at the feeding side (sub-station) of this transformer. The problem at our side may be due to flashover at substation. Second question is if there is some flashover on surge arrestor. Is it possible to check it whether it can be used again or not? In fact we changed it with new one as we didn't want to take any risk.
From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Internet Explorer 6.0 Fix
Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!