Temp Control Mode: Frame V Turbines

R

Thread Starter

Rahul P Sharma

During the normal operation of a Frame V turbine, the exhaust temp control set point is referenced against the PCD value...

But what is it (exhaust temp control set point) referenced to during the start up time when bleed valves are full open and PCD is zero (or nearly zero)? I've seen our MARK II control often switch between start up, temp control modes during the start up phase...

au revoir
Rahul P Sharma
 
You should have a warm up period where exhaust temp is regulated to 550 F. When the warm up expires, acceleration control takes over. Check your temp control calibration parameters for more information

Little known fact. Temp control is the only signal that can drive VCE to ZERO.
 