Member Login
member
passwd
remember me on
this computer.

- join now -
- forgot username or password? -

Search

Jump to a Date

Sponsored Communities
Cool stuff
Select a topic of interest:
...and press:
Neat Stuff
Control.com Stuff

Visit our shop for nerds in control lifestyle products.

Fortune
Frisbeetarianism, n.:
The belief that when you die, your soul goes up the on roof and
gets stuck.
RSS Feed
RSS feed Use this link to get an RSS feed of the Control.com article flow, for private, non-commercial use only:
www.control.com/rss/
To get a personalized feed, become a member at no cost.
Select a Page Style
Select one of the following styles:
- BluFu
- Classic
(cookies required)
advertisement
from the Power department...
Synchronous generator
Motion control, servos, steppers, etc. topic
Posted by Barnaby Prietto on 20 August, 2008 - 11:42 pm
The current will increase if an synchronous generator is made to work at 60 Hz and then is used at 50 Hz.

Will the stator current increase if an synchronous generator is made to work at 60 Hz and then is used at 50 Hz?

And the voltage will decrease?

What changes must be done for this change of frequency? Not only on the revolutions.

hecto7 at yahoo. com


Posted by jojo on 26 August, 2008 - 4:32 pm
Unfortunately you did not give much details of the generator you have at hand. So the info given below is generic but still applicable to your case. Forget the approach you are taking. The following needs to be taken care of when changing the operating speed of a generator:

1. you should not exceed the design magnetic flux in the core. To ensure this you have to maintain the same V/f ratio, where V is the nominal generated voltage of the generator, and f is the operating speed when the generator is running at nominal real power load and nominal power factor. Given the frequency is reduced, the voltage needs to be reduced also. You need to work out the design generated emf when the generator is running at full load and 60Hz, and then lower this voltage as indicated above.

2. (1) above then brings in the question whether the setting range of the AVR you have can be set to operate in automatic mode within the range of 78% to 91%. Normally the AVRs' range lies from 95% to 110% of nominal voltage.

3. The generators windings' and magnetic circuit cooling is done by fans fitted onto the shaft. Given the fans will be running at lower speeds, and thus a lower cooling air flow will be present, you will have to lower the maximum current that will be passing through the stator and rotor windings, such that insulation temperatures do not exceed design limits.

At the end of all this you are going to end up with a generator which will most probably not be able to be loaded more than 75% of its original design capacity. Is it worth the effort?

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!