Has anyone out there had any success with a serial interface between Allen Bradley's Control Logix to an Emerson Ovation DCS?
If so how did you do it? i know there are better ways but it is part of NERC CIP compliance.
There are a number of people who make protocol converters that should do what you want, and since it is an Allen Bradley PLC you should probably start with ProSoft who have a special relationship with A/B (see http://www.prosoft-technology.com/prosoft/products/for_rockwell_automa tion)
that includes providing protocol converters to Rockwell itself.
...but I have a question. Why is connecting a ControlLogix PLC to a DCS part of the NERC CIPs? I don't recall seeing a requirement to do that, and many utilities are doing exactly the opposite to avoid having to declare that they have cyber critical assets at all. I'd be interested in your answer, seriously.
By NERC standards, you can not have any routeable remote systems back to the DCS. Therefore, she'd have to use either serial or Profibus in order to achieve communications.
Ann,
we have an Emerson ovation system talking modbus RTU with serial links to an ABB AC410 system, a Nalco trasar unit, and several RS485 networks with SEL devices on them. I also talk to several SLC500 processors, but I use the Ovation TCP/IP driver for these. Not sure if I can help but I would be glad to share any knowledge I have if it helped you.
Hello MAKEVI
Can I use Ovation TCP/IP driver to get data from ovation DCS? Please any information like communication manual about it can I get from you?
Thanks in advance.
my email is yjdoo28 [at] bnftech.com
Doo
Thanks in advance.
Doo
Were you able to establish communication between the control logix plc and the ovation DCS? of so, how did you do it? do you have a screen shots of how you did that I can look at? I am currently working on such communication and don't know how to do it. I would really appreciate any help you can provide me.
Thanks,
Alex
260.667.7500
alexbaloch [at] yahoo.com
Thanks,
Alex
260.667.7500
Ann,
Do you have a document that show how this serial or Ethernet communication is done between Ovationa and Allen-Bradley Control Logix
Alex
Alex
Ann,
I have no specific experience with the problem as stated, but I suspect that the connection between the ControlLogix and Emerson DCS could be made.
Does the Ovation DCS support Allen Bradley's DF1 serial protocol?
According to this sheet, it seems to...
http://www2.emersonprocess.com/siteadmincenter/PM%20Power %20and%20Water%20Documents/pws_002864.pdf
If the Ovation DCS speaks DF1, then that would be one possible way of data exchange between the two systems.
If not, there are expansion cards for the ControlLogix that will give it Modbus support, such as those from ProSoft that Walt Boyes mentioned above.
Also, if you have some PLC selection flexibility... It's noteworthy that Allen Bradley's entry-level MicroLogix has pretty good native support for Modbus, whereas the higher-end ControlLogix does not.
Also, there are external, din-rail-mount protocol gateways that can do the job, too. I'm partial to the "Digi One IAP", which can perform protocol translation between various serial and ethernet protocols, including Modbus/RTU/ASCII/TCP and Allen-Bradley DF1 and EtherNet/IP.
Hope this helps!
Jim.
Hope this helps!
Jim.