Flow meter with pressure and temp compensation
Continuous process industries, DCS questions. topic
Posted by Chris on 23 July, 2009 - 4:53 pm
In the nickel refinery fluid bed reactor I'm working on, there's a volumetric flow meter VERIS Verabar V510 (element) with a SMAR LD301 remote mounted transmitter.

The process gas being measured is compressed air. I understand why the temperature compensation as density of air changes with temperature and hence so does volumetric flow.

But why is there pressure compensation incorporated into this flow measurement?

Thanks


Posted by Roy Matson on 24 July, 2009 - 11:52 am
Density also changes with pressure.


Posted by Chris on 24 July, 2009 - 3:44 pm
so volumetric flow meters don't require temperature/pressure compensation, only when the pressure and temperature of the process remain constant?



Posted by Syukri on 3 August, 2009 - 7:15 am
Theoritically if the Pressure and Temperature remain constant, Pressure and Temperature can be neglected but in the nature of gas, Pressure and Temperature will not be constant (effected by environemt and affected by process condition).

Furthermore, Verabar is a Pitot Tube type of Flowmeter which fall under pressure differential type of measurement. So I would say that P&T transmtter is compulsory for the Volumetric Flow measurement.


Posted by anynomous on 30 July, 2009 - 7:10 am
Boyle's LAW -

PV=nRT

enjoy


Posted by JMW on 4 August, 2009 - 1:42 pm
Let's start at the beginning.

Let's assume you want to know the volume flow rate. The instrument you have reports rate of flow in volume units. Temperature and pressure may well affect the density such that for the same volume flow rate the mass flow rate will differ according to the temperature and pressure.

However, you need also to consider the effect of temperature and pressure on the flow instrument. For example, increasing temperature will cause the instrument to expand and in expanding it will contain a larger volume of gas.

The same is true of pressure, the pressure will cause the meter to expand slightly and contain a larger volume of gas.

Thus, 1 cubic meter of gas measured at low temperature and pressure is recorded as 1 cubic meter but at a higher temperature and pressure that same 1 cubic meter of gas may be recorded as slightly less than 1 cubic meter.

Therefore the flow meter may itself require correction for temperature and pressure effects even if it is measuring only the actual volume flow.

Therefore, when considering temperature and pressure effects it isn't simply a case of the effect on density (liquid or gas) but the effect on the sensor.


Posted by Faisal on 5 August, 2009 - 1:31 am
Pressure will also change.


Posted by Anup on 14 April, 2012 - 1:01 am
Can anybody tell me the calculations for pressure and temperature compensation using any example?


Posted by Atul Wagh on 7 January, 2013 - 4:55 am
Density is function of both pressure and temperature...

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
How much does it cost to entice a dope-smoking UNIX system guru to
Dayton?
-- Brian Boyle, UNIX/WORLD's First Annual Salary Survey
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive