Has anyone successfully integrated a WDPF Grp1 QLC card to an Allen Bradley 1770 KF2 Module??
If So,
* what driver did you load onto the QLC card??
* what did the "configuration file" look like??
Any assistance will be much appreciated,
If So,
* what driver did you load onto the QLC card??
* what did the "configuration file" look like??
Any assistance will be much appreciated,
Hello, have you reviewed the information in Westinghouse Manual U0-1130?
Yes we have. To start you would need an older laptop with a 9 pin serial port. You will need DOS 5.0 or lower. We used DOS500 to create a dos boot disk. You can't do it through windows. The best is a 16 bit machine. You will then need to get a copy of ABQLC.exe, BACFLASH.exe and EXTPC.exe. These files must be loaded on the QLC card.
The QLC card will nned to be formated as a system drive. Here is an example of the file you will need to create:
/FILE: title = "Centrifuges 1&3",
port = 1 ,
baud = 9600,
parity = N,
databits = 8,
stopbits = 1,
sourceaddr = 10,
looptime = 0.0,
timeout = 2.0,
numnaks = 3,
numenqs = 3,
watchdogtime = 5.0,
switch = 0,
recoveryerrs = 3,
quiettime = 5.0,
statusreg = 2000
/GROUP: name = "C1 DIGITAL INPUTS 1",
direction = IN,
type = PLC-5,
station = 1
/DATA: SAL-5044A, N10:0.0, D0100
SAH-5044A, N10:0.1, D0101
SADL-5045A, N10:0.2, D0102
XA-5047A, N10:0.3, D0103
XA-5048A, N10:0.4, D0104
TAH-5042A, N10:0.5, D0105
TAHH-5042A, N10:0.6, D0106
TAH-5042C, N10:0.7, D0107
TAHH-5042C, N10:0.8, D0108
TAHH-5048A, N10:0.9, D0109
TAH-5043A, N10:0.10, D0110
TAHH-5043A, N10:0.11, D0111
TAH-5043C, N10:0.12, D0112
TAHH-5043C, N10:0.13, D0113
/GROUP: name = "C1 ANALOG INPUTS 1",
direction = IN,
type = PLC-5,
station = 1
/DATA: SI-5044A, N10:4, A0300
SI-5045A, N10:5, A0302
II-5047A, N10:6, A0304
II-5048A, N10:7, A0306
EI-5047A, N10:8, A0308
EI-5048A, N10:9, A0310
TI-5040A, N10:10, A0312
TI-5040C, N10:11, A0314
TI-5041A, N10:12, A0316
TI-5042A, N10:13, A0318
TI-5042C, N10:14, A0320
TI-5043A, N10:15, A0322
VI-5038A, N10:16, A0324
VI-5038C, N10:17, A0326
VI-5039A, N10:18, A0328
VI-5039C, N10:19, A0330
Create an autoexec.bat file using the file name like: abqlc -f test.txt -a Save this to the flash drive by typing bakflash on the B: move switch 6 up and reset the card. When connecting to the QLC card with the laptop, if you boot up the laptop with a dos disk, it is much faster when you type extpc and then reset the qlc card. The QLC should be set up on the switches for 9600 baud and switch 6 should be down so you can program the unit. After you back flash the B: drive you should raise switch 6 so the QLC will run your autoexec file. The -a allows you to see the program run with the laptop. If there are any errors this will tell you where they are. It takes about 2 hours to do this process and test your program
The QLC card will nned to be formated as a system drive. Here is an example of the file you will need to create:
/FILE: title = "Centrifuges 1&3",
port = 1 ,
baud = 9600,
parity = N,
databits = 8,
stopbits = 1,
sourceaddr = 10,
looptime = 0.0,
timeout = 2.0,
numnaks = 3,
numenqs = 3,
watchdogtime = 5.0,
switch = 0,
recoveryerrs = 3,
quiettime = 5.0,
statusreg = 2000
/GROUP: name = "C1 DIGITAL INPUTS 1",
direction = IN,
type = PLC-5,
station = 1
/DATA: SAL-5044A, N10:0.0, D0100
SAH-5044A, N10:0.1, D0101
SADL-5045A, N10:0.2, D0102
XA-5047A, N10:0.3, D0103
XA-5048A, N10:0.4, D0104
TAH-5042A, N10:0.5, D0105
TAHH-5042A, N10:0.6, D0106
TAH-5042C, N10:0.7, D0107
TAHH-5042C, N10:0.8, D0108
TAHH-5048A, N10:0.9, D0109
TAH-5043A, N10:0.10, D0110
TAHH-5043A, N10:0.11, D0111
TAH-5043C, N10:0.12, D0112
TAHH-5043C, N10:0.13, D0113
/GROUP: name = "C1 ANALOG INPUTS 1",
direction = IN,
type = PLC-5,
station = 1
/DATA: SI-5044A, N10:4, A0300
SI-5045A, N10:5, A0302
II-5047A, N10:6, A0304
II-5048A, N10:7, A0306
EI-5047A, N10:8, A0308
EI-5048A, N10:9, A0310
TI-5040A, N10:10, A0312
TI-5040C, N10:11, A0314
TI-5041A, N10:12, A0316
TI-5042A, N10:13, A0318
TI-5042C, N10:14, A0320
TI-5043A, N10:15, A0322
VI-5038A, N10:16, A0324
VI-5038C, N10:17, A0326
VI-5039A, N10:18, A0328
VI-5039C, N10:19, A0330
Create an autoexec.bat file using the file name like: abqlc -f test.txt -a Save this to the flash drive by typing bakflash on the B: move switch 6 up and reset the card. When connecting to the QLC card with the laptop, if you boot up the laptop with a dos disk, it is much faster when you type extpc and then reset the qlc card. The QLC should be set up on the switches for 9600 baud and switch 6 should be down so you can program the unit. After you back flash the B: drive you should raise switch 6 so the QLC will run your autoexec file. The -a allows you to see the program run with the laptop. If there are any errors this will tell you where they are. It takes about 2 hours to do this process and test your program
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.