Time synchronization in DCS system
Communications systems and equipment. topic
Posted by jianjian2112 on 15 October, 2009 - 5:39 am
Hi all,
Could some one explain to me about time synchronization in DCS system from GPS as following question:
How often does DCS system receive time synchronization signal in a hour? And how long is it between received times?
Posted by Ahmed on 15 October, 2009 - 12:48 pm
jianjian2112,
the target of time synchronization in DCS from GPS that if we have more than one controller system ,so by default each system will have its clock adjusted basically from the PC which downloaded the program in the system ,so if any trip or trouble occur in the system if all the system doesn't have the same time ,the reports will be messy and confused about at which time the problem occur due to difference in reporting time.
So a main controller or using GPS signal to every controller is sent in a specified time to every system in which every system readjust its clock.
and this signal is to be one (pulse signal) per day (or according to customer needs)
Hope you got the point,
Ahmed
Posted by Y.K.JARIWALA on 16 October, 2009 - 2:00 am
We are not very sure , but time synchronization plays very critical role in Multiple Node system we are not sure about GPS
typically, time synchronization cycle varies from DCS to DCS
HONEYWELL - EXPERION C300 10-100 ms
YOKOGAWA - CS3000 - 100 ms
This is Global system parameter , it has to synchronise simultaneously & top-most priority as far as the operating system Controller.
You have to specifically ask this parameter from DCS vendor.
This also plays very critical information , when on ETHERNET Highway , No of Nodes increases more than 8.
You may please varify this data from DCS vendors.
Jari
iconcnl [at] vsnl.net
Posted by Ketan Lakhani on 17 October, 2009 - 4:29 am
I feel that it is firstly required to understand as to why the synchronization is required. Generally for a critical continuous application which has more than one control system (e.g. DCS, PLC, UCP etc) communicating with master control system, requires the time synchronization. I remember earlier days, it was DCS which was used as Master Control System and use to send the Time Synchronization Pulse to all its subsystems. And this was done only to the systems which it was communicating.
Now a days, there are cases where you have multiple systems working independently (e.g. Process control System viz. DCS & PLC, Vibration Monitoring System, BMS, F&G, Well SCADA etc). If this is the case, then it is worth using GPS for time Synchronizing. GPS will give pulse at a specific time period(to be defined based on the accuracy of the clocks of every system) to all / any of the system. This will ensure that all the systems will have the same time and the analysis of the parameters(which created the disturbance) is accurate. E.g. Trip condition (accuracy is very important in this case as to what made the area/plant/unit trip and what was the exact time sequence).
Ketan Lakhani
Posted by mjak on 22 October, 2009 - 3:50 am
The system clock for most systems nowadays are very unlikely to drift more than a seconds in a day. For this reason, we sync the time of our DCS and subsystem only once per day. Unless your have a time critical requirement which require all the system to be in sync, then you may consider to do it more frequent.
Posted by M.Bhaskar on 25 October, 2009 - 11:51 pm
Hi All,
DCS system receive time synchronization in form of Pulse which can be defined for second and available through Serial ports which can be configured for IRIG-B port or Ethernet port. Normally each GPS do parallel tracking with satellites for time synchronizing and provide pulse per second output. Please make sure when you are buying GPS it must support NTP (network type protocol) to connect multiple devices on Ethernet like slave clocks, PLCs ,RTUs etc. if you want to have first hand information visit any 415KV substation to get exact details like GPS, Time stamping, and SOE details.
Posted by jianjian2112 on 11 November, 2009 - 10:12 pm
Hello all,
Thanks for all have taken care and explained for me.
And now we have another related GPS problem need to clarify: In the DCS system, which one of stations should be connected to GPS is the better way? History Data Server, Engineering station, configuration server, calculation server, real time data server or directly to the bus?
Thanks for all again!
Best regard!
Posted by M.Bhaskar on 12 November, 2009 - 7:36 am
please connect GPS to DCS directly through PPS or Ethernet in turn DCS will sync all other devices which are connected. One more option is connect GPS to LAN using NTP. All other devices which are connected in automatically get sync
Best regards
M.Bhaskar