GE turbine generator and open delta connection
Power generation equipment control. topic
Posted by serpi1981 on 19 October, 2009 - 11:57 pm
Hello I'm an electrical protection engineer.

I was trying to look for information about why the voltage transformers are open delta connected in a Ge design and if it has something to do with the LCI start up? maybe it has something to do with the 89nd switch and the need to be unearthed during the start up?

The reason why the machine working as a generator is grounded is because they need to limit fault current to a low value for a phase-ground fault to avoid damages to the machine(they limit to a typical value of 10A)?

The reason why it can not be ungrounded is because in case of a fault high transient over voltages appears in the machine deteriorating insulation materials. So in order to protect the generator they reduce both voltage transients and current fault values?

I hope this helps could you guys also answer my question?
Thanks in advance


Posted by CSA on 20 October, 2009 - 4:25 pm
How would you connect the potential transformers (I'm presuming you're talking about the ones used for synchronization purposes)? Isn't open delta sufficient for synchronization purposes? Doesn't it reduce the amount of wiring required to just three wires for two voltage sources?

As for the rest of the post, I'm not sure if you're asking or commenting. I think you're mostly correct on most of the items.


Posted by Phil Corso on 21 October, 2009 - 12:07 am
Serp1981...

Reur your question about open-delta xfmrs...
the reason is economic, that is, only two transformers are required instead of three!

Reur question about disconnecting the NGR... see: http://control.com/thread/1240942296!

Regards, Phil Corso


Posted by serpi1981 on 3 November, 2009 - 4:17 pm
Thanks for your answers the second part of the initial answer was the reply to an old post so don't worry about it.

I've heard about the open delta connection and know how it works, it is more common in USA, I'm used to wye-wye connected voltage transformers for electrical protections but when the supply of a gas turbine comes from GE usually they use that connection in the voltage transformer a custom and an economic issue I think you are right.

A friend of mine told me the LCI needs a system totally ungrounded, so the voltage transformers cannot be wye connected and the neutral earthing must be removed too for starting up the gas turbine I'd like to know if this is points is true or if it depends on the manufacturer. If you could help me It would be ok


Posted by Phil Corso on 4 November, 2009 - 9:29 am
Serpil981... the PTs should not be disconnected.

Only the NGR is disconnected for the acceleration period during which the the generator operates as a synchronous motor!

Regards, Phil Corso

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Support bacteria -- it's the only culture some people have!
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive