Modbus addressing for Function code 01
Power generation equipment control. topic
Posted by shailendra singh on 20 November, 2009 - 3:18 am
If we are using function code 01 for reading Booleans and from slave side address given 40010, then what will our starting address be 10 or 10*16? and also when we writing coils?


Posted by M Griffin on 20 November, 2009 - 5:50 pm
Coils are simply numbered consecutively from 0 to 65535 (or 1 to 65536, depending on whether you start counting at 0 or 1).

If you are using 40010 to mean holding register 10, then your question is about whether the device you are dealing with is "overlaying" coil addresses on register addresses and "packing" coils into registers. If that is the case, it is up to the device manufacturer as to how they do that. Typically, I would expect 16 coils to be packed into each register, but there is no absolute requirement for the manufacturer to do that. You need to consult the device documentation for details on that.

I have a brief explanation at the following web site that might help you with this:

http://mblogic.sourceforge.net/mbapps/ModbusBasics-en.html

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
I could dance till the cows come home. On second thought, I'd rather
dance with the cows till you come home.
-- Groucho Marx
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive