Hello all,
I have a communication problem between FI830F(ABB) as master and IM153-1(Siemens) as slave.
There is AC800F with FI830F DPV1 profibus module as master and ET200M with IM153-1 profibus module as slave. I did the following:
-Import GSD file(IM153-1_DPV1) to ABB,
-Test profibus cable and connectors
-set terminator in FI830F and last nod to ON (distance=200m)
-set address on each IM1531-1 from 2 to 7(i have 6 Node)
-set baud rate to 500Kb/s and even lower
At the plausibility check for in Control Builder i have no error but in commissioning mode,i receive "communication fault" in master and "No DigiNet-S- Communication" in slaves.
Thanks