high indication contact as normally close and low for normally open

X

Thread Starter

xx

I see always high switch are given for normally close contact and low switch for normally open is there any reason.
 
W
This configuration makes the switch de-energized to trip/alarm, i.e. the high switch normally closed position (energized) will open (de-energize) when a high condition exist and the low switch normally open position will close in the normal operating position (energized) and open on a low condition (de-energized).

William (Bill) L. Mostia, Jr. P.E.
Sr. Consultant
SIS-TECH Solutions

This information is being provide on a Caveat Emptor basis.
 