I am needing a bit of assistance if at all possible regarding a MKV EX2000 Sync problem.
We had ran the unit earlier in the day and shut down with no issues noted or any Breaker prot. alarms. During our second start, we reached 3600 rpm with no issues and attempted to Auto Sync the unit. All of our permissive indications were green and our voltages, frequency, and speed were in just the same state as our other units that were synced just fine. During a closer inspection, at the PTBA board, I was able to monitor the latching relays as they cycled during sync. I did notice that as the relays cycled, they were not in time with the sync scope as shown on Cimplicity.
The Cimplicity breaker close timer indicator continues to count up but the breaker never actually attempts to close. During this time I have no alarms about the breaker or failure to close, etc. I do get a turbine sequence incomplete and a TCE breaker timer out of limits alarm.
I surely hope that someone has seen something similar to this. I have tried the old reboot of our HMI's, Breaker rack out, etc.....
The difficult thing about this, is that we can't test this without actually firing the unit and getting to 3600 rpm. If there is another way for us to thoroughly test out our circuit without firing that would be great too!
Thanks very much for any assistance!
B. Grave
We had ran the unit earlier in the day and shut down with no issues noted or any Breaker prot. alarms. During our second start, we reached 3600 rpm with no issues and attempted to Auto Sync the unit. All of our permissive indications were green and our voltages, frequency, and speed were in just the same state as our other units that were synced just fine. During a closer inspection, at the PTBA board, I was able to monitor the latching relays as they cycled during sync. I did notice that as the relays cycled, they were not in time with the sync scope as shown on Cimplicity.
The Cimplicity breaker close timer indicator continues to count up but the breaker never actually attempts to close. During this time I have no alarms about the breaker or failure to close, etc. I do get a turbine sequence incomplete and a TCE breaker timer out of limits alarm.
I surely hope that someone has seen something similar to this. I have tried the old reboot of our HMI's, Breaker rack out, etc.....
The difficult thing about this, is that we can't test this without actually firing the unit and getting to 3600 rpm. If there is another way for us to thoroughly test out our circuit without firing that would be great too!
Thanks very much for any assistance!
B. Grave