from the blank wall department...
taking data from quantum plc modbus tcp in dh+ net
Communications systems and equipment. topic
Posted by sunil rathaur on 22 May, 2011 - 6:46 am
Sir,
we have dh+ network of ab plc 5/60 standard. recently we have installed Quantum DCS with Modbus tcp/ip . we would like to bring its data on dh+ bus in the main administrative building located at 1 km away and show it on PC with Rs view 32 HMI. please tell us how to go for it in the simple and cheapest way.
Posted by Wassim Daoud on 24 May, 2011 - 10:52 am
You can do this easily with OPC. All you need is OPC Data Manager to connect both systems together.
http://www.matrikonopc.com/products/opc-data-management/opc-data-ma nager.aspx
You might also need an OPC Server for each protocol as well. If you don't have them, download them from here for free:
Modbus OPC Server:
http://www.matrikonopc.com/opc-drivers/opc-modbus/base-driver-detai ls.aspx
Allen Bradley OPC Server:
http://www.matrikonopc.com/opc-drivers/opc-Allen-Bradley/base-drive r-details.aspx
Hope this was helpful
Cheers,
Wassim
Posted by James Ingraham on 25 May, 2011 - 5:49 pm
GridConnect / FactoryComm has the PKV6000 Modbus TCP to Data Highway Plus gateway. Sounds like a perfect fit. Also much easier than trying to maintain a PC with an OPC bridge.
http://www.factorycomm.com/gc-pkv4500-mbtcpdhp.html
Fieldserver also has an Ethernet to DH+ Gateway, but they don't specify that it's Modbus/TCP.
DataLink Technologies has the GW1000-MODTCP Modbus/TCP to DH+ gateway.
http://www.datatechgateways.com/gw1000-modtcp/
I'd have sworn SST / Woodhead / Brad / Molex had one, but I can only find the Ethernet to Profibus, not DH+.
I've never tried any of these products.
-James Ingraham
Sage Automation, Inc.
Personifiers Unite! You have nothing to lose but Mr. Dignity!
Advertise here