Hi,
Recently i've stumbled upon a low sensing pressure switch that confuse me about NO and NC contact. the wires is connected to common and NO terminal. When pressure is above 16bar (normal required condition), contact is OPEN. Contact closes when pressure below 16.
From what i understand in RELAY, NORMALLY is when coil is not energized. So normally open is CONTACT OPEN when coil not energized.
So, what is the general definition of "NORMALLY" in process switches? is it not the same with RELAY? or did manufacturer defines "NORMALLY" differently?
thanks