CPD and P2 transmitter fail notification

M

Thread Starter

Mark-V learner

Hi,

i would like to know if anyone of the CPD or P2 transmitter fails. we are not getting alarms or detection in the Mark-V. Is it possible to create an alarm or making rung so if anyone of the transmitter fails?

pls give me the suggestion and guide to make it.
 
B

Bob Johnston

I'm surprised you don't have anything to alarm on a CPD or P2 failure.
For P2 there normally is a Block L3GFLTV1 - Gas Fuel Control Fault, in there, there should be a P2 failure, usually (L3GFIVP) when P2 falls below LK3GFIVP usually set at -5 psi.

For CPD, there is usually a fault L3TFLTX when CPD is less than CAKCPD usually set at 70 psi.

The above is for a Frame 6, but should be roughly the same for any Frame size.
 
If your concern was failure of one of redundant transmitters, you should get a "high deviation" alarm when one transmitter differs from the other 2 by a significant amount. I don't remember what the settings are, but you can find them in the GE control specification.
 