We have Speedtronic Mark IV+ control system for controlling GE Frame 9 Gas turbine machine.
When I was stroking the Liquid fuel bypass valve after shutdown, I found that valve position is not going as per forcing voltage. for example if I give (+5 vdc) the valve is going only to 45 % closing (it should be 50%). When I am giving 8 vdc (full stroke) it is only going to 82% (it should be 100%). Both physical indication plate (which is not linked at all to LVDT) and LVDT reading on HMI are showing the same.
If I am giving more voltage also (around 9 vdc) the valve is closing more, at around 9.5 vdc the valve will close 100%.
My question is: I have to calibrate the servovalve? Or it should be replaced?
And if I am going to calibrate this one, what is procedure for that?
Regards,
When I was stroking the Liquid fuel bypass valve after shutdown, I found that valve position is not going as per forcing voltage. for example if I give (+5 vdc) the valve is going only to 45 % closing (it should be 50%). When I am giving 8 vdc (full stroke) it is only going to 82% (it should be 100%). Both physical indication plate (which is not linked at all to LVDT) and LVDT reading on HMI are showing the same.