Inquiry about cable size difference and its problems

S

Thread Starter

sreenath

sir,

i'm a qc inspector-instrument. while inspecting i find a problem in our h2s skid. the problem was that the instrument cables we are having is that 10p*.5mm only, but as per the vendor design it should be 10p*1.5mm. will that result in a problem if we are connecting the cables we have (10p*.5mm)?
 
B

bob peterson

It is unlikely the size will make any real difference if they are just signal cables. The smaller cables may not be as sturdy as the larger ones.

--
Bob
 
Top