We have GE Make 6FA Gas Turbine equipped with DLN 2.0 combustion technology which is being controlled by Mark V Control System. Recently we had finished our Combustion Inspection (CI), as a part of CI we had replaced the hot gas path parts like
Flow sleeves, Combustion Liners, Transition pieces,Fuel nozzles, etc.,with reconditioned pieces. DLN Tuning was performed by GE and following constants were changed,
FXKPTSP_1 85 --> 85.5 %splt (Premix Steady State Split %Split IGV Temp control on Array)
FXKPTSP_2 89.5 --> 89 %splt (Premix Steady State Split %Split IGV Temp control on Array)
FXKPTF_4 2350 --> 2330.6 deg F (Premix Steady State Split TF IGV Temp control on Array).
We had changed all our Moog valves (SRV,IGV, GCV's) with same part no (there was no problem in existing moog valves-it was working good but eventhough we had changed it) & its filters. Before replacing the servo we checked the resistance of new SRV and Splitter and it reads 1.084, 1.085, 1.091 KOhms for SRV and 1.05, 1.05, 1.06 KOhms for Splitter.After the replacement of new servos, stroke check were performed and found feedback is under the limit. No cards were replaced.
Due to GT Inlet gas pressure problem, we had requested GE for Auto unload sequence and implemented the same. Compressor inlet TC's were changed due to false reading and new TC's are working good.
The problem is that we had started the unit and reached the baseload (66MW) and found the MWATT was hunting between 2 to 3 Mwatts. All control valves like SRV (54.00 to 56%),Secondary (62 to 65.5%), Splitter (82 to 83%), Quat (25 to 27%) are fluctuating , due to that the parameters like FSRN, FSRT, TTXM, TTRF1 (+/-8deg C) & all Spreads are fluctuating (+/-6deg C).
CPR, CTD, AFQ are reading good and no fluctuation. IGV LVDT calibrated due to high difference between command and field position (measured locally) and no fluctuation. Checked the Prevoted values for MWATT Transducer and found all are reading almost the same values.
We suspected the DLN Tuning constants would create this problem and we had put back the old values and found no change in fluctuation (not helpful, keeps on fluctuation). Physically checked for Hydraulic Oil leakage in Gas compartment and found no leak.
We had taken the unit to preselect load just to check whether it is fluctuating or not, but it was fluctuating in that mode also.
Again taken the unit to Baseload and selected FSR MANUAL Control to determine whether the load hunting is caused by SRV or GCV's, in that we found Quat and Secondary valve stops fluctuating, but Premix splitter (FSGX) and SRV continues the fluctuation. (primary valve was in purging)
This issue had been taken to GE and they were suspecting the Servo of SRV and suggested to change the gain of SRV which they are thinking it too high (10.1), but the same gain was there in earlier Servo valve and we did not face any issues with that.
Can anyone help me to solve this issue?
1. What is making the MWATT to hunt?
2. What we need to do in offline to solve this issue?
3. Is there any temporary solution (like changing the constants in online, etc.,) to avoid this hunting until we plan for shutdown?
4. If we operate with this load swing what are all the parts may affect, is it advisable to operate with this load swing?
I am happy to provide you more inputs if you require.
Thanks in advance,
A2A.
Flow sleeves, Combustion Liners, Transition pieces,Fuel nozzles, etc.,with reconditioned pieces. DLN Tuning was performed by GE and following constants were changed,
FXKPTSP_1 85 --> 85.5 %splt (Premix Steady State Split %Split IGV Temp control on Array)
FXKPTSP_2 89.5 --> 89 %splt (Premix Steady State Split %Split IGV Temp control on Array)
FXKPTF_4 2350 --> 2330.6 deg F (Premix Steady State Split TF IGV Temp control on Array).
We had changed all our Moog valves (SRV,IGV, GCV's) with same part no (there was no problem in existing moog valves-it was working good but eventhough we had changed it) & its filters. Before replacing the servo we checked the resistance of new SRV and Splitter and it reads 1.084, 1.085, 1.091 KOhms for SRV and 1.05, 1.05, 1.06 KOhms for Splitter.After the replacement of new servos, stroke check were performed and found feedback is under the limit. No cards were replaced.
Due to GT Inlet gas pressure problem, we had requested GE for Auto unload sequence and implemented the same. Compressor inlet TC's were changed due to false reading and new TC's are working good.
The problem is that we had started the unit and reached the baseload (66MW) and found the MWATT was hunting between 2 to 3 Mwatts. All control valves like SRV (54.00 to 56%),Secondary (62 to 65.5%), Splitter (82 to 83%), Quat (25 to 27%) are fluctuating , due to that the parameters like FSRN, FSRT, TTXM, TTRF1 (+/-8deg C) & all Spreads are fluctuating (+/-6deg C).
CPR, CTD, AFQ are reading good and no fluctuation. IGV LVDT calibrated due to high difference between command and field position (measured locally) and no fluctuation. Checked the Prevoted values for MWATT Transducer and found all are reading almost the same values.
We suspected the DLN Tuning constants would create this problem and we had put back the old values and found no change in fluctuation (not helpful, keeps on fluctuation). Physically checked for Hydraulic Oil leakage in Gas compartment and found no leak.
We had taken the unit to preselect load just to check whether it is fluctuating or not, but it was fluctuating in that mode also.
Again taken the unit to Baseload and selected FSR MANUAL Control to determine whether the load hunting is caused by SRV or GCV's, in that we found Quat and Secondary valve stops fluctuating, but Premix splitter (FSGX) and SRV continues the fluctuation. (primary valve was in purging)
This issue had been taken to GE and they were suspecting the Servo of SRV and suggested to change the gain of SRV which they are thinking it too high (10.1), but the same gain was there in earlier Servo valve and we did not face any issues with that.
Can anyone help me to solve this issue?
1. What is making the MWATT to hunt?
2. What we need to do in offline to solve this issue?
3. Is there any temporary solution (like changing the constants in online, etc.,) to avoid this hunting until we plan for shutdown?
4. If we operate with this load swing what are all the parts may affect, is it advisable to operate with this load swing?
I am happy to provide you more inputs if you require.
Thanks in advance,
A2A.