Hello,
one of new GT turbine generator drive frame 5 mark VI controller during making the auto synchronization for the first time the scope in HMI is 180 degree different than the scope on GCPP panel and the breaker didn't close.
Also diagnostic alarm appears during that :
VTUR slot 4 diagnostic alarm <R><S><T> fault code 52 and the message (synch check relay slow that adjustment limits).
so the auto synchronization failed after that we stop the unit .
the diagnostic alarms still appear when the unit is stopped .
Thanks