We have a 2.5MW DG in parallel with a 20MVA transformer (UAT of a 250MW CCPP) (6.6kV). We want to run the 2.5MW DG in continuous parallel with the trafo. In the event of the UAT failing, can the non critical loads be switched off and DG continue to feed the critical loads?
As of now we have provided a df/dt relay which senses the UAT supply. On sensing UAT failure can the contact of this relay be used to trip all breakers of non critical loads and also incomer from UAT?
Is it necessary to ascertain separately whether the DG can withstand the load during the time between sensing of df/dt relay and tripping of the breakers?
Is there anything else to be seen before operating the DG in parallel with UAT. DG Set controller has got the facility for synchronising, limiting load to 2.5MW etc.?