I have been reading through a number of the generator islanding posts here on control.com, which have been very helpful (especially input from CSA!) however I believe the setup at my work is slightly different, and would appreciate an opinion on how the system would respond in the event of becoming islanded.
First, some details of our system. We have our own 33kV distribution system, to which one 140MW (third party owned and operated), three 17MW and two 28MW generators are connected. We also are connected to the National Grid via two 275/33kV transformers. Usual site operation is that we export ~90MW to the National Grid, importing ~50MW when the 140MW generator is offline. The site is therefore self sustaining when the 140MW generator is online and we are separated from the grid.
The five smaller generators generate at 11kV and are stepped up to 33kV by dedicated unit transformers. They are all driven by steam turbines, backpressure machines - the electricity output is effectively a 'byproduct' of them being used to let steam pressure down from 130bar to 14bar. They were installed in 1965, however they all have new AVR systems (the 17MW machines utilise Brush A50 AVR's, the 28MW use Alstom DX21's).
As far as I am aware, the generators are run up in speed governing mode, then set to pressure governing when synchronised to the network. These machines often operate in parallel - usually one or two 17MW machines run with one 28MW in service.
The operators adjust the MW setpoints to maintain the pressure in the 14bar steam system. The AVR's generally operate the 17MW machines overexcited to produce around +5MVar, and the 28MW around 21MVar.
The AVR's do not have communication between each unit, or 'islanded' detection. They are set to have a voltage droop of 5% which I believe should reduce the reactive power flow between the machines in the event of becoming islanded (both National Grid connections out of service).
My question is how the 17/28MW generators will likely respond upon loss of both grid connections, with the 140MW generator in service (thus site is net exporting power), and out of service (net importing). The 140MW generator does detect loss of grid, and goes into frequency control mode should this happen.
Could anyone provide any advice? The backpressure element of the generators is a concern for me, as I don't think they can be operated on-line in speed governing mode.
Please let me know if I can provide any clarification / more information!
First, some details of our system. We have our own 33kV distribution system, to which one 140MW (third party owned and operated), three 17MW and two 28MW generators are connected. We also are connected to the National Grid via two 275/33kV transformers. Usual site operation is that we export ~90MW to the National Grid, importing ~50MW when the 140MW generator is offline. The site is therefore self sustaining when the 140MW generator is online and we are separated from the grid.
The five smaller generators generate at 11kV and are stepped up to 33kV by dedicated unit transformers. They are all driven by steam turbines, backpressure machines - the electricity output is effectively a 'byproduct' of them being used to let steam pressure down from 130bar to 14bar. They were installed in 1965, however they all have new AVR systems (the 17MW machines utilise Brush A50 AVR's, the 28MW use Alstom DX21's).
As far as I am aware, the generators are run up in speed governing mode, then set to pressure governing when synchronised to the network. These machines often operate in parallel - usually one or two 17MW machines run with one 28MW in service.
The operators adjust the MW setpoints to maintain the pressure in the 14bar steam system. The AVR's generally operate the 17MW machines overexcited to produce around +5MVar, and the 28MW around 21MVar.
The AVR's do not have communication between each unit, or 'islanded' detection. They are set to have a voltage droop of 5% which I believe should reduce the reactive power flow between the machines in the event of becoming islanded (both National Grid connections out of service).
My question is how the 17/28MW generators will likely respond upon loss of both grid connections, with the 140MW generator in service (thus site is net exporting power), and out of service (net importing). The 140MW generator does detect loss of grid, and goes into frequency control mode should this happen.
Could anyone provide any advice? The backpressure element of the generators is a concern for me, as I don't think they can be operated on-line in speed governing mode.
Please let me know if I can provide any clarification / more information!