Rosemount Level transmitter Trouble
Sensor technologies. topic
Posted by Benjamin on 2 March, 2013 - 6:19 am
please I like to ask why is my Rosemount 3100 Level transmitter readings seems wrong (Lower than expected) even when my tank level is high?


Posted by David on 2 March, 2013 - 7:47 pm
If the readings are always low, then the reference level point and the bottom level points are suspect.

If your zero level is configured correctly, then a long shot is speed of sound effects: temperature or vapor composition/density. But I think this is a setup/configuration issue.

Is the error constant? How big is the error?

What are the level points used?

Is the tank pressurized? Vapor blanket? What is the temperature inside the tank?


Posted by Mirza Vaseem Raza on 6 March, 2013 - 5:20 am
The reading is low it means the range values went wrong..so it is better to calibrate both zero and span trim ...
And clean the sensor before calibrating..


Posted by Martin on 12 March, 2013 - 12:20 pm
Is the tank vented or sealed?

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Good leaders being scarce, following yourself is allowed.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive