Dear Colleagues,
After completion of GE frm6's Major overhaul we experienced unexplainable vibrations during startup which, reach their maximum at FSNL:
-Both seismic sensors of turbine brg indicated: 13.4 mm/s @ FSNL
-Both seismic sensors of compressor brg indicated: b 7 mm/s @ FSNL
By measuring the vibration using 2 other different external instruments, the values became 3.5 mm/s in turbine brg side and almost similar values in compressor brg which were considered acceptable.
So we proceed as follow to trouble shoot the problem:
-Replaced the 4 seismic sensors by other good ones
-Secured firmly the 4 probes
-Installed a new temporary shielded cable directly from field to control panel(MKV)
-Checked the configuration of TCQA in IO Config.
-Checked the revision of this card and compared with the IO configuration
-Replaced the TBQB card in MKV panel
-Checked all signals of TCQA in DIAG
-Checked for grounding in MKV
All these checks which were found normal led us to a slight improvement, the values changed form 13.4 to 9 mm/s in turbine bearings and 6mm/s in compressor bearing.
I share with all of you this weird problem in order to achieve to a convincing solution to this problem.
Thanks for all.
After completion of GE frm6's Major overhaul we experienced unexplainable vibrations during startup which, reach their maximum at FSNL:
-Both seismic sensors of turbine brg indicated: 13.4 mm/s @ FSNL
-Both seismic sensors of compressor brg indicated: b 7 mm/s @ FSNL
By measuring the vibration using 2 other different external instruments, the values became 3.5 mm/s in turbine brg side and almost similar values in compressor brg which were considered acceptable.
So we proceed as follow to trouble shoot the problem:
-Replaced the 4 seismic sensors by other good ones
-Secured firmly the 4 probes
-Installed a new temporary shielded cable directly from field to control panel(MKV)
-Checked the configuration of TCQA in IO Config.
-Checked the revision of this card and compared with the IO configuration
-Replaced the TBQB card in MKV panel
-Checked all signals of TCQA in DIAG
-Checked for grounding in MKV
All these checks which were found normal led us to a slight improvement, the values changed form 13.4 to 9 mm/s in turbine bearings and 6mm/s in compressor bearing.
I share with all of you this weird problem in order to achieve to a convincing solution to this problem.
Thanks for all.