Wonderware InTouch Alarms

T

Thread Starter

Tommy Tollin

When you put the Alarm display control window in your application in InTouch, and choose which tags you want to show as "alarms." example; if you want to regulate the level in a tank, you want an alarm condition if the level is below 10%. Then the alarm would pop up in the Alarm display control and you could Acknowledge it. but when the alarm is off (higher than 10%), then the alarm (tag) would not be displayed in the Alarm display control.. So my question is: How do u choose to let the alarm stay in the display window when it's still off, so you have time to acknowledge it and do your things? It just disappears when the alarm condition is off, kind of annoying.
 
If you open the properties of the alarm control window, under the query tab you have a query type option. if you set it to historical rather than summary, your alarms will stay there until you acknowledge and suppress them.
 