First off, do not connect the RJ45 to an Ethernet adapter. It will *probably* break something. To connect, you'll need either the old PIC Module (1747-PIC, requires a real serial port and WinXP Pro SP2 or earlier), or their USB version (1747-UIC). IIRC, the latter is only supposed to work at one baud rate so it may not work for you.
- You have to use these equipment/software:
* AB 1784-PCMK card complete with windows driver
* AB 1784-PCM4 cable
* RSLinx software
* RSLogix 500
or
* AB-1747 UIC complete with windows driver
* Straight thru UTP cable with RJ45 connector
* RSLinx software
* RSLogix 500
<pre>- If you use 1784-PCMK
* Configure RSLinx driver using PCMK for DH+/DH485 devices driver.
With PCMK option selected, then select DH485 for network type and enter baudrate, and station number.
* Then click OK
* If configured successfully, your DH485 network will displayed all of active network including your SLC-03
- If you use 1747-UIC
* Configure RSLinx driver using DH485 UIC devices driver, then entry station number and COM port no that will be use by 1747-UIC (use free com port).
* Then click OK
* If configured successfully, your DH485 network will displayed all of active network including your SLC-03