Polling a Modbus Slave

J

Thread Starter

JBB

i got some problem in setting up the Modbus communication in my system.

if i poll 1-50 register then no error but if i poll more than 60 then i got the error.
polling 1-50 then 51-100 digital input is fine.

but polling 1-100 input the error occur.

any idea???

thanks,
jojit
 
S
Sounds like either your master or your slave doesn't want to return more than 50 registers at a time (probably the slave, because if the limitation was in the master, it probably wouldn't let you set up the larger transaction). This is not too uncommon.
 
W

William \(Bill\) L Mostia Jr PE

What error did you get?

William (Bill) L. Mostia, Jr. PE
Fellow
SIS-TECH Solutions, LP
Any information is provided on Caveat Emptor basis.
 