in servo regulators what is meant integrator convergence gain (i/o config constants). how much value we have to set for proper operation of valve?
 
vm,

That value, while field-adjustable, is not meant to be "tuned" in the field. It is a factory-determined value which is used to keep the regulators in a TMR control panel from drifting apart by too much under normal operating circumstances.

It should be left as found.

If you provide more information about the type of turbine (Frame size; model number; etc.), the version/generation ("Mark" number) of the Speedtronic turbine control panel, the device which is driven by the particular servo-valve (regulator) output, perhaps we can tell you if the value you found in the field is the appropriate value as determined by GE.

Also, if you describe the problem(s) you are experiencing, perhaps someone here could help you with some troubleshooting or resolution suggestions. Remember when writing to a forum like this, we don't work with the equipment at your site every day like you do. We can't even see the equipment at your site. The more information you can provide in your original posting for help or information the more likely the initial response(s) you receive will be more concise and helpful, and the fewer questions you will likely be asked to answer to be able to provide more useful information. Help us to help you, is what I'm trying to say!
 