Parallel Generator

N

Thread Starter

natanael25

I have 2 generator with 12.5 kW power with steam turbine, and I want to parallel them both for reability purpose ( to support each other).

Which is the better system, isochronous-isochronous or isochronous speed drop, regarding that if i use isochronous-isochronous, i need to buy digital woodward governor.
 
Will these two generators be synchronized to a grid with other generators?

If yes, then they should both be in droop speed control.

If no, then only <b>one</b> prime mover should have an Isochronous governor and that machine must be started and loads first, and then the other machine (running in droop speed control mode) can b synchronized to the isoch unit.
 