Station trafo of our power plant tripped on standby earth fault (51N) when a nearby ICT was charged. mThis is a P633 relay (Now marketed by Schneider).
ST rating is 80/40/40 MVA 220/11.5/11.5kV. HV Star with neutral solidly grounded. LV1 and Lv2 neutral are grounded with Neutral Grounding resistor of 300 Ohms.
The setting of the standby earth fault is given as 0.1*In with a delay of 2 seconds. Where (In) is The HV neutral current. CT located in the HV neutral is 250/1 A.
There have been cases of tripping of transformers on differential protection due to inrush current of the transformer getting charged.
But here, due to charging of some other transformer in vicinity, our transformer gets tripped and that too on Standby earth fault.
It is not understandable that since the effect of inrush is for a few milliseconds, the relay still picked even after having a time delay of 2 seconds.
Can anyone please analyse. I shall be really thankful for advice.
ST rating is 80/40/40 MVA 220/11.5/11.5kV. HV Star with neutral solidly grounded. LV1 and Lv2 neutral are grounded with Neutral Grounding resistor of 300 Ohms.
The setting of the standby earth fault is given as 0.1*In with a delay of 2 seconds. Where (In) is The HV neutral current. CT located in the HV neutral is 250/1 A.
There have been cases of tripping of transformers on differential protection due to inrush current of the transformer getting charged.
But here, due to charging of some other transformer in vicinity, our transformer gets tripped and that too on Standby earth fault.
It is not understandable that since the effect of inrush is for a few milliseconds, the relay still picked even after having a time delay of 2 seconds.
Can anyone please analyse. I shall be really thankful for advice.