24V ac power supply can be laid with control cables in same conduit.

P

Thread Starter

prem sagar

i need to know is it possible that 24 v AC power supply can be laid with same conduit with control cables? as we are using it for damper actuators for dampers where we requires 24 V ac and 0 to 10 v dc for our control and feed back by using the same conduit.

my mail id [email protected]
 
usually you can run them in the same conduit (certainly the case for DC solenoids) but not the same cable bundle.

be sure to used shielded analog cables and keep the 24v ac grounds separate from the signal commons and shield connections for the analog signals.



 
P
we are using two types of cables for 24 vac we are using unshielded one and for controls shielded one, which is already protected. is it correct?
 