ViproS activated mismatch alarm

T

Thread Starter

toumi

Hello;

PLS we have an activated alarm MK6 from viproS and after the diagnostic check we found this activated ALM"G1/L4ETR1_FB voting mismatch =====and=== TRIP RELAY ETR CONTACT 01 MISMATCH REQUESTED STATE". we tried to RESET the vipro from the toolbox but it seem that the alm is activated,

PLS could you advise me.
 
Hello,

The <S> VPRO is also called <Y>.

Since the VPRO trips the turbine if an overspeed is detected OR if the rate of change of the turbine speed exceeds a pre-programmed level it's likely there's a problem with the speed pick-up providing the signal to <Y>.

There should be other Diagnostic Alarms associated with the <Y> VPRO to help troubleshoot and resolve the problem.

There are also some discrete inputs to the trip card (TREG for a gas turbine) that could be causing a problem--but that should also result in one or more Diagnostic Alarms for that and the other two VPRO cards in the <P> core.

Have you tried giving the unit a Master Reset from the HMI? (No; it should not trip the turbine if it is running and a Master Reset is initiated for the HMI. That presumes the other Process- and Diagnostic Alarms are all understood.)

When all else fails, you could try re-booting the <Y> VPRO by cycling the <Y> power switch in the <PD> core. (No; this should not result in a turbine trip if the unit is running if all the other Process- and Diagnostc Alarms are understood.) switch the power off; wait about 20-30 seconds; then switch the power back on.

If that doesn't resolve this issue, provide a comprehensive list of Diagnostic- and Process Alarms and be prepared to replace the VPRO with a spare VPRO.

Please write back to let us know how you fare.
 