Hi all,

I'm new to the area and trying to find out the dynamical response of the terminal voltage of a synchronous generator to a sudden breakdown of a transmission line connecting the generator to a motor, assuming the generator is unregulated and has constant mechanical power supply.

Due to the size of network we are simulating (about 120 nodes (generator/motor) and 200 edges (transmission line)), a simplified model (e.g. a differential equation) capturing the most dominant feature is enough.

Any ideas are welcomed!
ZXZ
 
S

Sebastian Rebord

ETerm = Eq + jITerm*Xd, where:
ETern: Terminal Voltage
ITerm: Terminal current
Eq: Generator's internal Voltage (it could be greater or lower than the terminal voltage depending if it is running over or under excited)
Xd: Synchronous reactance (X'', X', X, depending the span of time you are seeing after the disturbance).

As you can see, if a generator is running overexcited, because you said it has a motor as load, the field voltage is constant (unregulated), after loss the load (for example: 52G open), the terminal voltage will rise up to equal Eq (not as step, because you have the different time constants T''do, T'do).

Regards
 