Call up group trend in Honeywell Station

M

Thread Starter

Mostafa Qasemi

I want to call a group trend in station by push button in Hmi.
I set a push button and filled action "systnd03.htm", but it goes to first group. and when I wanted to go in second group, I type "2(systnd03)". it doesn't do any action. Although second group link is shown "2(systnd03)" in station!

Thank you so much
Best regards
 
If You have an Experion system you need to do following steps:

1. Add a new Button to display.

2. Go to Details section.

3. Change following parameters:
- Set to Request a task;
- Set parameter TASK LNR to 21
- Set Parameter1 to 8;
- Set Parameter2 to trend with you want.

That's all.

Regards
 
M

Mostafa Qasemi

Thank you so much. It works.

Can I do this for alarm list?

They want me to put a pushbutton that goes to alarm list which filtered by location.
For example first pushbutton goes to train1 alarms second goes to Esd alarms.....

I really need this thanks in advance.
Best Regards
 