Mr. Phil Corso Sir,
We started first time one used turbine alternator of M/S AEG Type S 7085 d4 6.3KV 20MVA. The phase rotation mentioned on name plate are VUW<-. The alternator rotation is anti clock looking from none drive end. There were six terminals with no marking coming out from alternator. I assumed reading from left to right in front of terminals these are U V W and X Y Z. Because of physical obstruction I made Star and ground to UVW and brought XYZ assumed L1 L2 L3 of 6.3KV brought out for supply.
I have had to synchronize these with a 20MVA transformer 6.3V/11KV. In synch check relay both generator and bus PT connected together in order of left to right Gen L1, L2, L3 and bus L1, L2, L3.
The unit synchronized with utility and running satisfactory but the protection relay is displaying Negative sequence voltage 100% and positive sequence voltage 0%. similarly -ve seq current 26% and +seq current 0%. Kindly suggest me where is I am doing something wrong? and how can I rectify it.
I shall be obliged.
Best Regards
Shaheed
I shall be obliged.
Best Regards
Shaheed