Hi everyone,
I wish to thank you for your time. Please I need your help to solve this question.
I have a standard distribution system (11kV) making use of an islanded power plant (generator output 11kV) (See link below). The loads for each section are: 0.7MW, 1.1MW, 1.1MW, 0.9MW. Ahead of these loads are transformers of type DYg (11kV/433V, 1500kVA). The other loads are directly connected to the 11kV distribution system and are: 0.6MW (combined load), 3.2MW (Sag Mill), and 5.6MW(Ball Mill). When the ball mill starts, it uses a liquid resistance starter that demands 1.8 times normal load.
I need to determine the number of sets required to start the Ball Mill with a fully loaded plant in two cases: using diesel sets or using gas reciprocating engines.
Diesel sets: 1250 kVA, 11 kV, 50 hertz, power factor 0.8 and inertia constant 50.2 kg-m², damping ratio = 0.13.
Reciprocating engines: 5175 kVA, 11 kV, 50 Hertz, power factor 0.8 and inertia constant 1300 kg-m², damping ration = 0.13.
What should I calculate to find the number of sets?
Thanks a lot for your help.
http://files.engineering.com/getfil...86&file=distribution_system_diesel_vs_gas.png