Please I need your advice for the following problem.
We have 4 Analog output signals 4- 20 mA sent by analog output card model ADAM 4024 has 4 channels connected to yokogawa DCS CENTUM VP analog input card model AAI143 (DCS is passive) .
When we try to connect the fuses and knife bridges of marshaling cabinet during the loop check and starting simulating mA on one channel of ADAM card, the other channels change also. the values of mA not match with what we simulate and the values we get in DCS (ranges are same in DCS and the field).
We make the following tests
1- We disconnect all the cables that connect between ADAM card and DCS except one channel (for example channel no 1). we measure the mA in series by multimeter we get 4 mA and this a correct values. we try to connect the wires of the other channels; we notice the value of mA increases to 8 mA. also when we connect just one wire positive or negative the value of mA change too, and this happened for all other channels when we repeat the same test on the remaining 3 channels.
2- we bring mA loop calibrator. we use it to measure mA in one channel. And connect multimeter in series with resistance box adjusted on 250 Ω. We notice that the two channels don't affect each other even if we increase the resistance until 1 kΩ.
Please, help me to find interpretation for the reason that make mismatching between the DCS and the ADAM card. and what we do to make this connection work.
Thank you
Please I need your advice for the following problem.
We have 4 Analog output signals 4- 20 mA sent by analog output card model ADAM 4024 has 4 channels connected to yokogawa DCS CENTUM VP analog input card model AAI143 (DCS is passive) .
When we try to connect the fuses and knife bridges of marshaling cabinet during the loop check and starting simulating mA on one channel of ADAM card, the other channels change also. the values of mA not match with what we simulate and the values we get in DCS (ranges are same in DCS and the field).
We make the following tests
1- We disconnect all the cables that connect between ADAM card and DCS except one channel (for example channel no 1). we measure the mA in series by multimeter we get 4 mA and this a correct values. we try to connect the wires of the other channels; we notice the value of mA increases to 8 mA. also when we connect just one wire positive or negative the value of mA change too, and this happened for all other channels when we repeat the same test on the remaining 3 channels.
2- we bring mA loop calibrator. we use it to measure mA in one channel. And connect multimeter in series with resistance box adjusted on 250 Ω. We notice that the two channels don't affect each other even if we increase the resistance until 1 kΩ.
Please, help me to find interpretation for the reason that make mismatching between the DCS and the ADAM card. and what we do to make this connection work.
Thank you