My gas turbine (GE Frame 9E) CPD dropped 0.5bar within 2-3 hours and load dropped at about 10MW. Prior to the incident, no work was carried out and no abnormal alarms were annunciated. The significant drop was partially due to higher ambient temperature. On a day to day operation comparison, the load supposed to dropped about 3-4 MW and not 10MW. The followings are inspections that we have carried out but to no avail:
1. Inspected bearing #2 venting and sealing piping and flange.
2. Checked waterwash isolation valves
3. Shut isolation valves of compressor bleed valves during baseload (no improvement of CPD or load)
4. Inspected all porous stone filters (FA-3,-4 and -6)
5. Performed boroscope inspection (no findings)
6. Inspected CPD transmitters
7. Inspected atomizing air line in accessories compartment
8. Inspected AD1
9. Inspected VIGV (measured at site)
10. Listened for noise during cruising down and cranking
11. Replaced VA-18 (found minor leak at piston)
12. Flame scanner gasket replacement
13. Atomizing air cooler - gasket replaced due to flange minor leak.
14. 20CB union joint tightened due to minor leak found
15. Air filters physical conditions and manometer readings.
16. Checked all the constants on HMI and compared with other GT. All normal.
17. False start drain
18. Bearing temperature (same before and after incident)
19. Inspected AE5
Ever since the incident, the gas turbine efficiency has dropped. We have also noticed that during FSNL before the incident, the CPD was at 6.4bars. After the incident, the CPD was at 6.9bars during FSNL. Troubleshooting is still being carried out. At baseload, we are only getting 9.8 bars instead of 10.3bars before. Although, the CPD was higher than before during FSNL. We appreciate any feedback.
My gas turbine (GE Frame 9E) CPD dropped 0.5bar within 2-3 hours and load dropped at about 10MW. Prior to the incident, no work was carried out and no abnormal alarms were annunciated. The significant drop was partially due to higher ambient temperature. On a day to day operation comparison, the load supposed to dropped about 3-4 MW and not 10MW. The followings are inspections that we have carried out but to no avail:
1. Inspected bearing #2 venting and sealing piping and flange.
2. Checked waterwash isolation valves
3. Shut isolation valves of compressor bleed valves during baseload (no improvement of CPD or load)
4. Inspected all porous stone filters (FA-3,-4 and -6)
5. Performed boroscope inspection (no findings)
6. Inspected CPD transmitters
7. Inspected atomizing air line in accessories compartment
8. Inspected AD1
9. Inspected VIGV (measured at site)
10. Listened for noise during cruising down and cranking
11. Replaced VA-18 (found minor leak at piston)
12. Flame scanner gasket replacement
13. Atomizing air cooler - gasket replaced due to flange minor leak.
14. 20CB union joint tightened due to minor leak found
15. Air filters physical conditions and manometer readings.
16. Checked all the constants on HMI and compared with other GT. All normal.
17. False start drain
18. Bearing temperature (same before and after incident)
19. Inspected AE5
Ever since the incident, the gas turbine efficiency has dropped. We have also noticed that during FSNL before the incident, the CPD was at 6.4bars. After the incident, the CPD was at 6.9bars during FSNL. Troubleshooting is still being carried out. At baseload, we are only getting 9.8 bars instead of 10.3bars before. Although, the CPD was higher than before during FSNL. We appreciate any feedback.