Hi,
Today we performed meter verification using field communicator 475 on Emerson flow-transmitter 1700 series installed on one of our gas turbine micromotion flowmeter F200S, to verify the meter calibration. Please note that the whole process was done on No-flow and full pipe condition.
We worked with online HART device option in which I connected HART communicator with flow transmitter device and automatically it detected the connected field device i.e. transmitter. Connection was successfully done and we saw all online menu available on field communicator device display for that flow-transmitter. We run Process Variable option and saw all the readings which the flow transmitter was displaying and it worked fine.
We have encountered an issue with meter verification selection. This option is available under menu Diagnostics and Service -> Calibration -> Meter Verification. When we selected this, communicator showed two-options to be selected i.e. 1) Last value 2) Fault. If we select any one of them, stiffness value was asked by the menu to be selected from a table enlisted as 0.1, 0.5, 1.0, 2.0, 3.0, 4.0, 5.0. Here we have no further information to proceed in correct way. Anyhow, we selected and run the meter verification, field communicator showed message on the display "meter verification error". What does that mean and what is the way out/corrective measure to do meter verification successfully?
Today we performed meter verification using field communicator 475 on Emerson flow-transmitter 1700 series installed on one of our gas turbine micromotion flowmeter F200S, to verify the meter calibration. Please note that the whole process was done on No-flow and full pipe condition.
We worked with online HART device option in which I connected HART communicator with flow transmitter device and automatically it detected the connected field device i.e. transmitter. Connection was successfully done and we saw all online menu available on field communicator device display for that flow-transmitter. We run Process Variable option and saw all the readings which the flow transmitter was displaying and it worked fine.
We have encountered an issue with meter verification selection. This option is available under menu Diagnostics and Service -> Calibration -> Meter Verification. When we selected this, communicator showed two-options to be selected i.e. 1) Last value 2) Fault. If we select any one of them, stiffness value was asked by the menu to be selected from a table enlisted as 0.1, 0.5, 1.0, 2.0, 3.0, 4.0, 5.0. Here we have no further information to proceed in correct way. Anyhow, we selected and run the meter verification, field communicator showed message on the display "meter verification error". What does that mean and what is the way out/corrective measure to do meter verification successfully?