We have PT-100 RTD's installed on our Motors. These RTD's are the trip security of motors and are terminated on P+F Barriers K-System KFD2-UT2-Ex1. The output of these barriers are connected to our emergency shutdown system (Prosafe RS PLC).
For some time, when we start a motor after a month or more (For test start up), the Motor Trips showing PLC Channel Fault. No high or Low temperature trip is shown on PLC. This fault appears in a split second. Surprisingly the same doesn't happen when we start the motor again after first tripping.
The motor runs smoothly in second attempt.
We have checked & swapped RTD's circuits in the area but found nothing. All RTD's that are causing tripping are separate, terminated on separate TB's and barriers and are on separate input cards of the PLC. Grounding wires of the RTD's are well connected.
Is there a fault in our loop or there is a problem with the sensor behaviour? There is no Timer in the logic. Why does the fault only occur when we startup a motor after a month or more and why does it only occur in less than a second? How does the fault disappear when the same Motor is started after first time tripping.
Please suggest a solution.
Thank You!
For some time, when we start a motor after a month or more (For test start up), the Motor Trips showing PLC Channel Fault. No high or Low temperature trip is shown on PLC. This fault appears in a split second. Surprisingly the same doesn't happen when we start the motor again after first tripping.
The motor runs smoothly in second attempt.
We have checked & swapped RTD's circuits in the area but found nothing. All RTD's that are causing tripping are separate, terminated on separate TB's and barriers and are on separate input cards of the PLC. Grounding wires of the RTD's are well connected.
Is there a fault in our loop or there is a problem with the sensor behaviour? There is no Timer in the logic. Why does the fault only occur when we startup a motor after a month or more and why does it only occur in less than a second? How does the fault disappear when the same Motor is started after first time tripping.
Please suggest a solution.
Thank You!