We are asked to calculate size of transformers needed to service 3 phase 4 wire high leg delta based on the assumption that the system would need to continue running even if one of the non center tapped transformers failed and was removed.
I know that for a balanced 3 phase load you just divide the total load by .866 then divide it by two and that's your transformers to keep working even if one of the three is lost and/or removed. When you center tap one of the three and add more load to it via 120 volt circuits, how do you calculate the upsizing needed for the one transformer to compensate? I am taking into consideration the compensation for open delta while supporting the 3 phase and single phase loads. I am looking for the formula and not a particular example.
I know that for a balanced 3 phase load you just divide the total load by .866 then divide it by two and that's your transformers to keep working even if one of the three is lost and/or removed. When you center tap one of the three and add more load to it via 120 volt circuits, how do you calculate the upsizing needed for the one transformer to compensate? I am taking into consideration the compensation for open delta while supporting the 3 phase and single phase loads. I am looking for the formula and not a particular example.