Fr-9E DLN 1 Unit just returned back from HGPI and fail to go premix transfer on Gas with high spread around 45 Deg C during the transfer from Primary lean to premix mode.
In last 3 attempts unit goes to extended lean lean mode.
Sequence of Operation - GE controls TA at site
Unit started normally reached 40% load - did liquid fuel transfer successful with all parameters normal. Again transfer to gas increase the load to 60% - lean lean mode with all parameters normal.
Change to liquid fuel - all parameters normal checked for both primary & secondary lines leaks - no issues noted.
Transfer back to Gas - start loading further.
Unit goes to extended lean lean operation during the transfer - premix operation was not successful. Spread noted observed around 45 deg C during the transfer. Primary all flames ON. unit was brought down to primary mode and again attempt to take unit to premix but no success again went to extended lean lean.
GE decided to make IBH ON this time and unit reached premix mode successfully without any issues. At baseload noted spread was around 38 Deg C, NOx around 33ppm & CO about 5ppm. GE control TA tried adjust the split to position at best possible to lower the NOx between 78% to 81%..unit goes to extended lean lean when tried to go below 79% or above.
GE TA confirmed issue with combustion system or the accessory components for the fact Unit unable to reach premix operation with IBH off.
It was decided to make Borescope on combustion components to understand any combustion hardware issues, however no indication found during borescope for any sign of secondary/primary fuel nozzles or Liners.
After discussion with GE engineering they recommended to replace all primary/Secondary fuel nozzles - which is under progress.
Same they suggest to perform leak test on primary & Transfer purge valves VA13-1, 2, 3 & 4 along with Transfer valve. this was done with GE site team. found no issues with Purge valves and transfer valve was sent to Fisher for testing and found leakage is within their acceptable limit. Calibration of all the valves was confirmed by GE control TA at site - no issues.
Just to Add - when unit was dis-assembled we found damage of secondary/primary fuel nozzles and liners #7 & 10 can were damaged but still unit was able to go premix operation with any issues before outage and spread maxmium of 28 deg c.
Now we are going for startup and would like to know from your experience any further advice? or anything to add part of solution?
Regards,
Arun.
Fr-9E DLN 1 Unit just returned back from HGPI and fail to go premix transfer on Gas with high spread around 45 Deg C during the transfer from Primary lean to premix mode.
In last 3 attempts unit goes to extended lean lean mode.
Sequence of Operation - GE controls TA at site
Unit started normally reached 40% load - did liquid fuel transfer successful with all parameters normal. Again transfer to gas increase the load to 60% - lean lean mode with all parameters normal.
Change to liquid fuel - all parameters normal checked for both primary & secondary lines leaks - no issues noted.
Transfer back to Gas - start loading further.
Unit goes to extended lean lean operation during the transfer - premix operation was not successful. Spread noted observed around 45 deg C during the transfer. Primary all flames ON. unit was brought down to primary mode and again attempt to take unit to premix but no success again went to extended lean lean.
GE decided to make IBH ON this time and unit reached premix mode successfully without any issues. At baseload noted spread was around 38 Deg C, NOx around 33ppm & CO about 5ppm. GE control TA tried adjust the split to position at best possible to lower the NOx between 78% to 81%..unit goes to extended lean lean when tried to go below 79% or above.
GE TA confirmed issue with combustion system or the accessory components for the fact Unit unable to reach premix operation with IBH off.
It was decided to make Borescope on combustion components to understand any combustion hardware issues, however no indication found during borescope for any sign of secondary/primary fuel nozzles or Liners.
After discussion with GE engineering they recommended to replace all primary/Secondary fuel nozzles - which is under progress.
Same they suggest to perform leak test on primary & Transfer purge valves VA13-1, 2, 3 & 4 along with Transfer valve. this was done with GE site team. found no issues with Purge valves and transfer valve was sent to Fisher for testing and found leakage is within their acceptable limit. Calibration of all the valves was confirmed by GE control TA at site - no issues.
Just to Add - when unit was dis-assembled we found damage of secondary/primary fuel nozzles and liners #7 & 10 can were damaged but still unit was able to go premix operation with any issues before outage and spread maxmium of 28 deg c.
Now we are going for startup and would like to know from your experience any further advice? or anything to add part of solution?
Regards,
Arun.