I work thermal power plant in South Korea.
We use Mark-VI for turbine control but we have a big problem with Mark-VI control. I want to solve the problem.
History is like this,
'15.02.041)Main TBN RACK0 <R> SLOT 12 VAOC DIAGNOSTIC ALARM
- Configuration with TMR, Analog Output <R> 1 Channel Mismatch ALARM
'15.03.012)Main TBN RACK0 <R> SLOT 08 VCRC DIAGNOSTIC ALARM
- Configuration with TMR, Relay Output <R> 1 Channel (Fault Code: 154)
-> Relay Changed, but nothing difference
'15.03.173)Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM (Fault Code: 46)
- VCMI Control Fail
-> RACK0 <R> VCMI Card Manual Reset(Push Reset Button in the card)
After VCMI Reset, (1)/(2)/(3) Alarm cleared
'15.03.183)Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM Re-generation (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM Re-generation (Fault Code: 46)
-> VCMI Configuration/Firmware Download and <R> phsor power Off/On
After Power Off/On (3) Alarm cleared
'15.03.183)Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM Re-generation (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM Re-generation (Fault Code: 46)
'15.03.19:RACK0 <R> VCMI Replaced -> ALARM Cleared
'15.03.222) Main TBN RACK0 <R> SLOT 08 VCRC DIAGNOSTIC ALARM Re-generation (Fault Code: 154)
(3) Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM Re-generation (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM (Fault Code: 46)
------------------------------------------------------------------
In the manual, VCMI Card Faults (57,67) are caused by sequencing overrun and then controller is failed. So we changed VCMI Card. But Alarms occurred again.
So we have a question. Please reply me.
1. Why the 'R' phasor VCMI Card Fault (Code : 57,67) occurred?
- In the manual 'control fail caused by sequence Overrun', why Overrun occurred?
2. In the fault code 'Controller Fail', why the UCVE in not alarm?
3. Why the 'R' phasor VCRC Fault(Code : 154) occurred?
- Always channel 10 alarm (we changed Relay, But alarming)
4. After 'Power Off->On'/'VCMI Reset', why the alarm disappeared? And Why the alarm?
We use Mark-VI for turbine control but we have a big problem with Mark-VI control. I want to solve the problem.
History is like this,
'15.02.041)Main TBN RACK0 <R> SLOT 12 VAOC DIAGNOSTIC ALARM
- Configuration with TMR, Analog Output <R> 1 Channel Mismatch ALARM
'15.03.012)Main TBN RACK0 <R> SLOT 08 VCRC DIAGNOSTIC ALARM
- Configuration with TMR, Relay Output <R> 1 Channel (Fault Code: 154)
-> Relay Changed, but nothing difference
'15.03.173)Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM (Fault Code: 46)
- VCMI Control Fail
-> RACK0 <R> VCMI Card Manual Reset(Push Reset Button in the card)
After VCMI Reset, (1)/(2)/(3) Alarm cleared
'15.03.183)Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM Re-generation (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM Re-generation (Fault Code: 46)
-> VCMI Configuration/Firmware Download and <R> phsor power Off/On
After Power Off/On (3) Alarm cleared
'15.03.183)Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM Re-generation (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM Re-generation (Fault Code: 46)
'15.03.19:RACK0 <R> VCMI Replaced -> ALARM Cleared
'15.03.222) Main TBN RACK0 <R> SLOT 08 VCRC DIAGNOSTIC ALARM Re-generation (Fault Code: 154)
(3) Main TBN RACK0 <R> VCMI DAIGNOSTIC ALARM Re-generation (Fault Code: 57,67)
Main TBN RACK0 <R> VSVO 4,11,16, DIAGNOSTIC ALARM (Fault Code: 46)
------------------------------------------------------------------
In the manual, VCMI Card Faults (57,67) are caused by sequencing overrun and then controller is failed. So we changed VCMI Card. But Alarms occurred again.
So we have a question. Please reply me.
1. Why the 'R' phasor VCMI Card Fault (Code : 57,67) occurred?
- In the manual 'control fail caused by sequence Overrun', why Overrun occurred?
2. In the fault code 'Controller Fail', why the UCVE in not alarm?
3. Why the 'R' phasor VCRC Fault(Code : 154) occurred?
- Always channel 10 alarm (we changed Relay, But alarming)
4. After 'Power Off->On'/'VCMI Reset', why the alarm disappeared? And Why the alarm?