Dear All;
The plant where I am, there are A, B, C and D turbo-compressors (GE MS5002 driving BCL CC). The D machine is experiencing Combustion Troubles. I already posted it on this forum and could be reached through this link: http://control.com/thread/1417205798 (Exhaust Temperature Spread MS5002D Gas Turbine).
My concern this time is not about the D machine but it's about the others machines. When investigating the root causes of the combustion trouble on this D machine, I observed that TNH of the others machines are fluctuating and in the same time their TTXSPL jump away from the initials values.
On machine B; TNH is changing value from 99,97% to 100,01% and back to 99,97%. If the time between the changes is greater than 120 seconds than the TTXSPL reading is about 57°C but when this laps is less than the 120 seconds (and it's the case mostly) TTXSPL jump and stay at 168°C.
As said most of time, the fluctuation in TNH occurs at below the 120 seconds and therefore TTXPL is almost equal to 168, 1 °C. <b>My concern is because the TTXSPL is too higher we'll NOT get Combustion Trouble Alarm even if a real trouble occurs.</b>
My questions are: Does 0,04% TNH fluctuation affect the Allowable Spread (TTXSPL)? If yes, what could be the root causes of this fluctuation and how to avoid it? How does MARK V logic works with same fluctuation?
One more detail: When TTXSPL changes value all the exhaust temperature thresholds will change also. See below.<pre>
TNH ------------- 100,01% --- 99,97%
TTXM------------- 521 °C --- 522
TTXSPL----------- 57,3 °C --- 168,1
TTHT------------- 547 °C --- 598
TTHA------------- 544 --- 589
TTLT-------------- 485 --- 416
TTLA-------------- 498 --- 455</pre>
Many thanks In Advance.
[email protected]
The plant where I am, there are A, B, C and D turbo-compressors (GE MS5002 driving BCL CC). The D machine is experiencing Combustion Troubles. I already posted it on this forum and could be reached through this link: http://control.com/thread/1417205798 (Exhaust Temperature Spread MS5002D Gas Turbine).
My concern this time is not about the D machine but it's about the others machines. When investigating the root causes of the combustion trouble on this D machine, I observed that TNH of the others machines are fluctuating and in the same time their TTXSPL jump away from the initials values.
On machine B; TNH is changing value from 99,97% to 100,01% and back to 99,97%. If the time between the changes is greater than 120 seconds than the TTXSPL reading is about 57°C but when this laps is less than the 120 seconds (and it's the case mostly) TTXSPL jump and stay at 168°C.
As said most of time, the fluctuation in TNH occurs at below the 120 seconds and therefore TTXPL is almost equal to 168, 1 °C. <b>My concern is because the TTXSPL is too higher we'll NOT get Combustion Trouble Alarm even if a real trouble occurs.</b>
My questions are: Does 0,04% TNH fluctuation affect the Allowable Spread (TTXSPL)? If yes, what could be the root causes of this fluctuation and how to avoid it? How does MARK V logic works with same fluctuation?
One more detail: When TTXSPL changes value all the exhaust temperature thresholds will change also. See below.<pre>
TNH ------------- 100,01% --- 99,97%
TTXM------------- 521 °C --- 522
TTXSPL----------- 57,3 °C --- 168,1
TTHT------------- 547 °C --- 598
TTHA------------- 544 --- 589
TTLT-------------- 485 --- 416
TTLA-------------- 498 --- 455</pre>
Many thanks In Advance.